There seems to be a tendancy now to wire single phase installations with 3 core SWA and ignore the armour as a conductore. What is the favoured way of installing 3 phase? 4 core T&N wth armour as earth, or 5 core TN&E? Indeed, is 35mm 5 core generally available?
 
Last edited:
Normally a 4core ,but if it was a long run you might have to run a seperate cpc so it might be an option to run a 5core if its in stock? also the cores might be white.So its down to calcs./spec./avai./& price

yours benji
 
I suppose if cost is important there is nothing wrong with using the armouring, as long as the locknuts are tight and don't corrode, work lose, ELI reads OK etc. Using 5 core eliminates this possibility so I would always go for 5 core, and have no problem getting hod of it.
 
I personally have never installed 5 core SWA and have only seen it once.

I can't see a problem in using the amour for a steel CPC and larger than 50mm cable running a seperated eath cable to reinforce the Ze

I think it comes down to personal choice,

I would say that if you base your costings for the more expensive option and the if the budget gets tight on the job, then you can change the spec for the cheaper option.

(this is assuming you haven't detailed the exact cable)

I think this is one for personal choice and there is no right or wrong answer

Richard
 
theres a reat page in GN1 that tells you if the SWA will be suitable for a CPC cant remember the page if i remmember correctly above 35mm 4c a seperate cpc has to be run and also some 16mm. double check first.
as for usinf a 5c remember the cpc can be smaller than live conductors so a seperate cpc will be cheeper.
 
If the installation is TN-S it would be prudent to lay a CPC of the same cross-sectional area as the conductors in a 4-core SWA cable in addition to securely bonding the wire armouring.
 
I've checked GN1 and it makes it quite clear that 35mm SWA has not just a little bit more than the required CU equivelent armour, but much more than adequate. Using 5 core or an additional earth is therefore not a requirement.

Regards,
Geoff
 
have been happy in the past to use 4 core although i find that 5 core often looks nicer and is generally a neater install.


although sometimes dependent on what you are doing the cost outways the pro's
 
I was under the impression that over a certain size of swa you cant use the armour as an earth and a seperate earth needs to be run in, unless there's a core for ie 5 core. personally never used 5 core and usually run in a seperate earth if needed. but always make sure that swa armour is earthed.
 
:cool: Thanks gaulty. Since the inception of 17th Edn. I have always run a suitable seperate CPC alongside TP&N 4-core SWA buried cables and also for 3-core TP cables. Most of my work is on rural services for private pumped water supply installations, so longer power supply cables are the norm in our business as water engineers. I think that your take on this shows a responsible attitude to earth bonding.

Regards, termite.
 
It's a pitty SWA cables are so crap now. Under M&Q and foundry regs no CPC is required. The cables had 1 tinned copper to 3 steel wires in the armouring. Better still install PILCDWA the return path was often better the conductors

Thank god I've retired :D
 
Last edited by a moderator:
OK. GN1 specifies that for 35mm SWA the armour is an acceptable CPC. But here comes the runt.
Irrespective of the Regs, (or is it in very strict adherence of the regs?) the MET must be at the supply head and the main bonding must run to the MET. It is unacceptable, and they will NOT provide a connection, if the bonding is to a Dis Board fed from a sub main.

Also, tails of more than 3 meters are Unacceptable. If the tails would be more than 3 meters then you have to install a single way DB (switch fuse or other) within 3 meters and take the sub main from that. More over, and contarary to the EDF web site which only requires an isolator, but only in some areas, it must contain fuses (or I suppose some other form of cutout) . The Reason... "so that they do not have to change their fuses if there is a fault with the sub main". ... Sounds rediculous to me because there is no discrimination, however that is their requirement before thay will connect a meter.
 
Last edited:
I was under the impression that the tables in GN1, that refer to sizes of armourings in SWA, were an indication to whether the armourings comply with table 54.1 (54G in 16th). If the armourings do not comply then the adiabatic equation needs to be done in order to ascertain whether the armouring are capable of taking the current produced under earth fault conditions.
 

Reply to SWA for 3 Phase Installation in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
690
If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking...
Replies
7
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
529
Hi there , is there anything else to consider when using 5 core SWA instead of 4 core + separate Earth in three phase installations for cable...
Replies
2
Views
881
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock