L
Lofty
Hi All,
Got a call today about a DB tripping over the week-end.
Narrowed it down to the switches and contactor for their outdoor pool. Now here's the issue.
The contactor (Old MEM 3P adjustable 4-8A) switches both the pool pump and the oil fired boiler (on the same contacts) via an old style Sangamo timeclock. All of which has been working fine for the last 10-15 years.
If both loads are disconnected from the contactor the contactor holds, however connect EITHER the boiler OR the pump and it takes out the RCD. All IR measurements on the contactor seem to be OK, and when it trips there's no visual signs i.e. arcing from the coil to earth.
Could it be the contactor failing under load ?.
Cheers,
Lofty.
Got a call today about a DB tripping over the week-end.
Narrowed it down to the switches and contactor for their outdoor pool. Now here's the issue.
The contactor (Old MEM 3P adjustable 4-8A) switches both the pool pump and the oil fired boiler (on the same contacts) via an old style Sangamo timeclock. All of which has been working fine for the last 10-15 years.
If both loads are disconnected from the contactor the contactor holds, however connect EITHER the boiler OR the pump and it takes out the RCD. All IR measurements on the contactor seem to be OK, and when it trips there's no visual signs i.e. arcing from the coil to earth.
Could it be the contactor failing under load ?.
Cheers,
Lofty.