codger

-
Reaction score
12
An armoured 90 degrees cable is to be installed between two pieces of equipment. The equipment at either end is rated at the standard 70degrees C. The cable was tested as a 70degrees cable but another organisation has said that the cable must be tested as a 90degree cable regardless of the equipment rating. Does this sound ok..?

Cheers
 
I don't follow the 'tested' part. In the situation u describe the cable is usually treated as running at 70 degrees and its ccc is the 70 degree one.
 
you need to explain a little better .

if you have specced a 90 degree cable and plan to run at 90 degrees you need to check with manufacturers that there equipment can handle the 90 degree temp .
 
If the equipment is only rated to 70ºC then the cable must be assessed on current carrying capacity and resistance (impedance) as only ever being able to run at 70ºC. Any variation of the values that may be present because it could run at 90ºC must be disregarded as it would never be safe to run it in this way.
 
An armoured 90 degrees cable is to be installed between two pieces of equipment. The equipment at either end is rated at the standard 70degrees C. The cable was tested as a 70degrees cable but another organisation has said that the cable must be tested as a 90degree cable regardless of the equipment rating. Does this sound ok..?

Cheers


As Richard stated...

The company you refer too, need to provide sound technical argument to make that sort of statement!! Otherwise you would need to assess virtually every SWA installation over the last 5 years or so for 90C compliance (whatever that means), as the majority of SWA cables supplied as standard by wholesalers over that time, have XLPE insulated conductors!!

From what i can make of it, you need to stipulate 70C PVC insulation when ordering these days...
 

Reply to Temperature rating of equipment. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
529
Hi All. What is the best/preferred method when connecting 20mm conduit to a back box of a socket on an outside wall ? I am connecting a BG...
Replies
10
Views
3K
Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
486
I have been asked/invited to "post more", lol, so let me make another post right away. I thought of sth worthy to post, of interest to many, I...
Replies
2
Views
510
My garden lighting was tripping my MCB so I checked all the junction boxes outside. I disconnected the live, neutral and earth connections in...
Replies
2
Views
901

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock