Well at least there was a strong Resistance, must have been a circuit of some sort.
you need to speak to Rene about the resistance... listen carefully. I shall only say this once.
Are you mistaking multimeters for the Multi Function Testers (MFT's) we use for installation testing, we still use the standard multimeters but these are not capable of carrying out the tests needed to verify an installation
You've got a good point, can't do a megohm test with a multimeter.
To be more specific, as an electrician (installer), we're not required to do these loop tests, megohm tests on houses, last I knew anyway. I have been required to do these in factories for certain circuits as well as for feeders. On some jobs, ie: power plants, chip fab plants; we did have crews "commissioning" EVERY circuit, including feeders.
There is a very strong requirement here for dead testing before the circuit is energized, both for a full installation and for simply adding a new circuit to an existing system. That applies for domestic, commercial and industrial stuff.
Not just IR testing to see if the cable is OK, but also testing R1+R2 (live and earth resistances) both to verify socket & SP switch polarity, and also from the boards Ze (earth loop impedance) to check the circuit's Zs value is going to allow fast enough disconnection by the choice of fuse or MCB, etc.
Reply to The Ring is dead, long live the Radial!⚡ in the UK Electrical Forum area at ElectriciansForums.net
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
4K