Spud28
Evening, has anyone got the current carrying capacity for old Tinned copper cables. Im looking at using an existing cable that looks just under 6mm (Imperial size most likely) for a cooker circuit. IR etc tests out ok. Thanks in advance.....
It is probably 7/.044 if it looks 6.0mm which is approximately 6.45mm so theoretically you can use 6.0mm ratings.
Reactions: Spud28
Thanks for the reply! Is there a chart or table as I would like to confirm on site. Cable definitely looks smaller than 6mm but bigger than 4mm. Cant seem to find any info....!
7/036 will be it then, I sent you a chart of sorts, I used that size for 30Amp circuits when I were a Lad, 7/029 was for ring mains as they were known in the past, the very distant past, Telectrix will know all about those cables as well as me and some of the oldies.
7/.036 it is, I misread the post as I thought it read larger than 6.0.
Reactions: Spud28
Brill, thanks a lot - do you have the CCC for this one then please? all I could find is a reference to fuse wire but I cant even find that now!!!
Its on the lists I sent you
Reactions: Spud28
See Pete's files in #3.
Reactions: Spud28
Reactions: Spud28
copy and file it you never know when might need it again .
Reactions: Spud28
already done ! Couldn't find the info anywhere, got it after five mins on here, really good!
It's a joy to see someone asking about tinned cu....so many of them think it's ally, these days.
all the young dudes will be asking next about pyro. how does that work. and do they teach them that a collage the old stuff .
..... Couldn't find the info anywhere....
At times think "Google" is getting more Dumb,
and ebay more expensive than the local shop !