ok, in a bit of a debate with myself here?!!
looked a t big extension on a bungalow, guy wants underfloor heating, already speccced it himself...................if thats what he wants to do, anyway, it looks like he wants two, one in the kitchen(2kw) and one in the downstairs showeroom, all part of the new build extension(1kw)

I will be fitting new board etc all fairly easy, so any suggestions on wiring the underfloor into the ccts.

Ie
1) do i wire a seperate radial for both approx 35 metres in total 2.5mm
2) do i wire into the ring, one on the kitchen ring(2kw) the other on the downstairs ring(1kw)
or do i wire it in 4.0mm for the radial? I know it only totals 3kw, however the guy may have a conservatory built next year and may want underfloor heating in it?? approx 2 kw?

what u think?

could even wire it all on a seperate ring as i have room on board, leaving scope to tap into it with conservatory next year.

its one of those, im unsure what i will have next year kind of jobs if u know what i mean!

Any opinions apprciated
 
Last edited by a moderator:
ok, in a bit of a debate with myself here?!!
looked a t big extension on a bungalow, guy wants underfloor heating, already speccced it himself...................if thats what he wants to do, anyway, it looks like he wants two, one in the kitchen(2kw) and one in the downstairs showeroom, all part of the new build extension(1kw)

I will be fitting new board etc all fairly easy, so any suggestions on wiring the underfloor into the ccts.

Ie
1) do i wire a seperate radial for both approx 35 metres in total 2.5mm
2) do i wire into the ring, one on the kitchen ring(2kw) the other on the downstairs ring(1kw)
or do i wire it in 4.0mm for the radial? I know it only totals 3kw, however the guy may have a conservatory built next year and may want underfloor heating in it?? approx 2 kw?

what u think?

could even wire it all on a seperate ring as i have room on board, leaving scope to tap into it with conservatory next year.

its one of those, im unsure what i will have next year kind of jobs if u know what i mean!

Any opinions apprciated

Think I'd go for that if you may need to add to the circuit at a later date.
 
thats what i was thinking bud......................looks like the best option, as like i said im expecting the call next year for the conservatory and im dead sure the guy will want the underfloor heating in there so best i plan for that me thinks!!!

cheers matey
 
Maybe just let the customer decide. Give him two quotes, one for the cheapest route and one for the option that will allow future connection for the conservatory.
 
I would go for seperate radials for each but I would want to look into the shower room as in you part p people just to see what they say as its 230 v and lots of water and I wouldn't want to do anything at all wrong in that case so make sure its best it could be according to them. More wine needed lol
Paul
 
should be ok in the shower room, its basically a small bathroom with a shower cubicle in it!
if u know what i mean.
 
should be ok in the shower room, its basically a small bathroom with a shower cubicle in it!
if u know what i mean.

As it is UFH it is classed as a special installation and will have to come under Part P as notification in any case regardless of where it is installed.
 
I would go for seperate radials for each but I would want to look into the shower room as in you part p people just to see what they say as its 230 v and lots of water and I wouldn't want to do anything at all wrong in that case so make sure its best it could be according to them. More wine needed lol
Paul

It's bs 7671 that determines how it is done,not part P......there is a section on general underfloor heating in section 7 and it's covered in locations with a bath or shower....as always check out the relevant regs before installing.
 
cheers guys, i will look into it and make sure that what i quote is within the regs.
think i will go for a seperate cct though, prob small ring to save the customer buying 4mm cable
 
It's bs 7671 that determines how it is done,not part P......there is a section on general underfloor heating in section 7 and it's covered in locations with a bath or shower....as always check out the relevant regs before installing.


I wrote that pressuming Pablo was struggling with the brb so they could advise him
Paul
 
cheers solo, im all good with the BRB.................was just trying to decide what was the best method really and looking for opinions! thank you anyway bud
I wrote that pressuming Pablo was struggling with the brb so they could advise him
Paul
 
cheers guys, i will look into it and make sure that what i quote is within the regs.
think i will go for a seperate cct though, prob small ring to save the customer buying 4mm cable

I thought RFCs where only for socket outlets?

What about a couple of radials in 2.5? You'd need an extra MCB, but save on one run of cable.
 
Regulation 533.1.5 tells that BS 1363 may be supplied by a ring final circuit, it does not say only BS 1363 can be used on a ring final. I have wired FCUs on a ring final, but I can't imagine wanting to fit much else on it, or any kind of fix load appliance.
 
Having looked into it, I agree that a ring final can be used for things other than sockets. I don't see the advantage though if you're only supplying 2 or 3 points.
 
its a bit of a do i dont i scenario!!
the total load of underfloor heating with potential new build of conservatory next year will be around 5KW.
the run is only about 25 metres in total. I have not fitted a board yet so can scope it out for a bigger one to accomodate the extra ccts.
ive gotta feeling the customer wants room for extra ccts for the future as he is going to stay in this place until he croaks it......................so he tells me! lol
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
underfloor heating!
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
ukpablo,
Last reply from
not clever,
Replies
15
Views
3,447

Advert