The supply to the house has an earth connected to the side of the house about 4m roughly above the meter, however no earth is present at the DNO's fuse/meter. Therefore I am unsure of where the earth goes from the fuse box without tearing the wall apart and searching through the cavity (a rather drastic and silly idea I think you'd agree).
And yes I did disconnect the cable before measuring.
I suppose it's technically possible that there is a separate MET hidden somewhere in the house, and that the earth wire from the fuse box goes there and then bonding from that MET is messing up my reading. However there is no separate MET anywhere for a few meters in any direction from the fuse box, there's no record of anything left from anyone who's previously done any work on the property, the owner isn't aware of another MET (not surprising), and so if there is another MET hiding somewhere my chances of finding it with the house still furnished... Well I'll take the needle in a haystack any day.
Can't the earth bar in a CU be used as the MET?you're right in that it was common for the earth bar in the fuse board to be used as a MET up till 16th ed ( 1991).
That's what I thought.I do lots of time.
Good question DNOs will quote typical values of 0.80 for TN-S and 0.35 for TN-C-S but these are not hard and fast and often quoted for new builds. Older networks may often exceed this.0.56 ohms is ok for TN-S.
Reply to Unsure About An Old Earthing Arrangement in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.