I was assuming that the 6mm² CPC was adequately sized.
With PME, the CSA is chosen so the conductor can withstand diverted neutral currents for long periods of time, rather than earth fault currents for short periods of time.
My view is that we cannot guarantee how much fault current will flow in which conductor so one should be sized to carry out the function solely.