Discuss Use of SWA armour as protective bonding conductor? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I was assuming that the 6mm² CPC was adequately sized.
With PME, the CSA is chosen so the conductor can withstand diverted neutral currents for long periods of time, rather than earth fault currents for short periods of time.


My view is that we cannot guarantee how much fault current will flow in which conductor so one should be sized to carry out the function solely.
 
There has been research and testing provided to the "industry" that goes along with the idea that the fault current will be shared acceptably by an internal core & the SWA, & / or an external cpc, the internal core & the SWA.
So you can do any of the above.
Also if you check GN1 you will get armour csa's for compliance with table 54.7, from this you should be able to assess your suitability.

Also you can use the adiabatic to size bonding conductors.

Not sure about being able to size main bonding by adaibatic with TNC-S paul? i think your allowed to on TNS & TT.
 
My view is that we cannot guarantee how much fault current will flow in which conductor so one should be sized to carry out the function solely.
Both as I understand it are sized adequately to carry the fault current.
The armour apparently is equivalent to 15mm2, with regards to k2/k1.
It's just the conductance equivalence that doesn't meet the requirements.
 
Lenny,
I understand your point, but one of the major players has commissioned research, and it has been done & published, it states that you are fine with the scenario I describe.
The research is on the internet somewhere, I think I also have it on my disk, but I can't look now sorry guys.
Wife's car has just broken down, why when we are skint!
Running on 3 cyls by the look of it, that's only half the engine, so big problems.
May be back later, or if I'm not around for a few days, sorry but I may be doing car mechanic type things!!!
 
Hi folks, attempting to fix a screw up by previous installer. TN-C-S domestic property with garage outbuilding. MET is in consumer unit in main house; garage distribution circuit protected by RCBO. Garage sub board populated with MCBs. Cable to garage is 6mm2 SWA 3 core. Garage has extraneous conductive parts. Equipotential bonding back to the relevant board exists in main house and in garage.

Here's the problem. The armour is not terminated to the MET in the main house but is terminated to the earth marshalling terminal in the garage sub board. The third core is used as the CPC for the distribution circuit to the garage. Table 54.8 requires a 10mm2 for the main protective bonding conductor. It's a posh property and adding in a parallel 10mm2 earth cable is going to be tricky. (I know I could add a rod but trying to avoid that just now). What I'd love to do is terminate the SWA armour properly and use it as the protective bonding conductor. Assuming that the SWA is BS3646, the equivalent CSA of the armour is 15mm2 (data from earthingnuts website) so it is of adequate size.

Does the above approach look ok? Do the regs restrict use of armour as protective bonding conductor? Many thanks.

I think there are several issues here.

Firstly, the ERA report is based on fault current sharing between the armour(cpc) and a parallel cpc. If the third core is used as a cpc then i dont see the ERA report being to much of a help.

The system is TNC-S, so if there are extraneous conductive parts with to be connected we need to consider the use of not just the armour as a bonding conductor but also the use of a core. This is due to the possible heating effect of the diverted neutral current which could cause the insulation to prematurely fail. One way to look at it is if the loading of the cable is low then the heating effects of any neural current will be limited.

If you decide that this is not an issue then we need to decide as Spin has mentioned whether we can use the combined CSA to satisfy the bonding requirements. I'm not aware of a regulation which says this is not an option. If we run two 6mms or a 10mm, i see no issue, the ECP'S are effectively connected to the met via a CSA required by the regs.

Where the Main Protective Bonding conductor is made up of the armour and a core, then in effect the ECP'S are connected to the MET with A CSA required by the regs.

I think this comes down to engineering judgement and what effect the diverted neutral currents may have on the cable, i think the issue is will it comply with Chapter 52?

Regards Chris
 
Last edited:
I elected to run new 10mm2 bonding cables and have spent the whole day doing it. My decision was based around the semi rural nature of the property, fed underground but overhead to pole transformer not far away. Risk of neutral loss is higher than an urban scenario and that swung it for me. If I was to come up with an analogy, the requirements for these large bonding conductors in TNC-S are like the provision of a protective barrier underneath a bridge in case a section of the bridge was to fall down: it feels like overkill but if the regs (and a strong body of opinion) agree with it, I would be challenging the status quo with my signature on a lesser solution. I have really enjoyed this thread; thanks to all who participated.
 

Reply to Use of SWA armour as protective bonding conductor? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock