I was assuming that the 6mm² CPC was adequately sized.
With PME, the CSA is chosen so the conductor can withstand diverted neutral currents for long periods of time, rather than earth fault currents for short periods of time.


My view is that we cannot guarantee how much fault current will flow in which conductor so one should be sized to carry out the function solely.
 
There has been research and testing provided to the "industry" that goes along with the idea that the fault current will be shared acceptably by an internal core & the SWA, & / or an external cpc, the internal core & the SWA.
So you can do any of the above.
Also if you check GN1 you will get armour csa's for compliance with table 54.7, from this you should be able to assess your suitability.

Also you can use the adiabatic to size bonding conductors.

Not sure about being able to size main bonding by adaibatic with TNC-S paul? i think your allowed to on TNS & TT.
 
My view is that we cannot guarantee how much fault current will flow in which conductor so one should be sized to carry out the function solely.
Both as I understand it are sized adequately to carry the fault current.
The armour apparently is equivalent to 15mm2, with regards to k2/k1.
It's just the conductance equivalence that doesn't meet the requirements.
 
Lenny,
I understand your point, but one of the major players has commissioned research, and it has been done & published, it states that you are fine with the scenario I describe.
The research is on the internet somewhere, I think I also have it on my disk, but I can't look now sorry guys.
Wife's car has just broken down, why when we are skint!
Running on 3 cyls by the look of it, that's only half the engine, so big problems.
May be back later, or if I'm not around for a few days, sorry but I may be doing car mechanic type things!!!
 

Reply to Use of SWA armour as protective bonding conductor? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
518
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock