Hi folks, attempting to fix a screw up by previous installer. TN-C-S domestic property with garage outbuilding. MET is in consumer unit in main house; garage distribution circuit protected by RCBO. Garage sub board populated with MCBs. Cable to garage is 6mm2 SWA 3 core. Garage has extraneous conductive parts. Equipotential bonding back to the relevant board exists in main house and in garage.

Here's the problem. The armour is not terminated to the MET in the main house but is terminated to the earth marshalling terminal in the garage sub board. The third core is used as the CPC for the distribution circuit to the garage. Table 54.8 requires a 10mm2 for the main protective bonding conductor. It's a posh property and adding in a parallel 10mm2 earth cable is going to be tricky. (I know I could add a rod but trying to avoid that just now). What I'd love to do is terminate the SWA armour properly and use it as the protective bonding conductor. Assuming that the SWA is BS3646, the equivalent CSA of the armour is 15mm2 (data from earthingnuts website) so it is of adequate size.

Does the above approach look ok? Do the regs restrict use of armour as protective bonding conductor? Many thanks.
 
The CSA of the armour does not have a conductivity equivalent to 15mm² copper.
What you are looking at in the earthing nuts website, is the thermal withstand equivalence based on the k2/k1 values.
The conductivity equivalence between copper and steel is about 9:1.
So you would have to divide the CSA of the armour by 9 to establish the conductivity equivalence.
Depending on what cable you have that would give an equivalence of 4mm²(PVC) or 2.5mm²(XLPE).
 
If i've read this post correctly, then you have said that the main equipotential bond in the garage is already in place, therefore you don't need the 3rd core in your SWA, to perform as your main bonding conductor, just your distribution cables CPC!!


Doesn't matter if the SWA is connected to the EMT or the MET , as they should both be connected together via the 3rd core of your 6mm SWA cable....


QUOTE: Garage has extraneous conductive parts. Equipotential bonding back to the relevant board exists in main house and in garage.
 
Last edited by a moderator:
If i've read this post correctly, then you have said that the main equipotential bond in the garage is already in place, therefore you don't need the 3rd core in your SWA, to perform as your main bonding conductor, just your distribution cables CPC!!


Doesn't matter if the SWA is connected to the EMT or the MET , as they should both be connected together via the 3rd core of your 6mm SWA cable....
Whilst bonding is in place in the garage, the conductor used to connect back to the MET in the house is only 6mm².
 
Whilst bonding is in place in the garage, the conductor used to connect back to the MET in the house is only 6mm².

Not sure what he means Spin, if he is talking about the SWA providing the bonding, or the bonding was in place originally, ....ie part of the original house install??
 
Many thanks guys. Yep, bonding from services in garage back to sub board in garage is ok, but I'm missing the all important 10mm2 from garage back to the MET. It's last chance saloon I think then, rod or parallel cable, unless any other offers on the table?
 
Many thanks guys. Yep, bonding from services in garage back to sub board in garage is ok, but I'm missing the all important 10mm2 from garage back to the MET. It's last chance saloon I think then, rod or parallel cable, unless any other offers on the table?

Ah ...sorry i must have misread your OP then!! ... In that case you really will need to get a 10mm from the EMT back to the MET, and there is really no way around that i'm afraid!!!
 
How old is the installation, is it pre 16th edition?
Is the SWA PVC or XPLE?
If I remember correctly, the minimum CSA required in the 15th for a main bonding conductor was only 6mm² for PME, as such I would apply a code 4 if there are no signs of heat damage.
If the SWA is PVC, then the combined CSA equivalence of the armour and the 6mm² CPC will be 10mm².
I must admit, that I don't like the fact that the armour is not earthed at the supply end.
I would check the Zs reading for the armour at the supply end.
 
Not sure of original install date - did the requirements for the 10mm2 bonding conductor we see now in table 54.8 exist in the 16th as well? If they did, client might be able to claim from a scheme operator. Many thanks.
 

Reply to Use of SWA armour as protective bonding conductor? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
521
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock