Hi guys,

i have changed a fuse board today in a outbuilding/large shed (it has a kitchen and shower and lounge etc.. a )

It is a TT system with earth rod.

My ZE reading was 187 ohms - now the regs state I am ok upto 200, so I assumed this was ok.

All the R1 + R2 and insulation resistance came back normal.

When I carried out the ZS tests, the reading were very high, for example:

Shower circuit on a 40a MCB - 2.6 omhs !
Kitchen Ring on a 32a mcb - 2.7 omhs !

same for lounge and bedroom rings.

I have checked to regs and these figures are over the maximum allowed.


Any advice ???
 
And was the ground wet? Ie in favourable conditions?

If so then you could try coupling two rods together if they are 5/8s.
 
max. Zs is 1667 ohms if 30mA RCD fitted to all circuits.
 
  • Like
Reactions: 2 people
I checked the date first but it's not April 1st.

What Zs readings would you expect on such a system with an Ra value of 187 Ohms?

Your bonding will have reduced Zs already but RCD protection will give you much higher max Zs figures depending on RCD ratings (up to 1667 Ohms for 30 mA)

You really need to brush up on the reg's before you undertake such work, clients are paying for your competency and skills...
 
  • Like
Reactions: 9 people
teletrix. just to confirm, you are saying the my readings were acceptable ? I understood that (on page 103 of osg) my maximum ZS for a type b 40a Breaker is .093 ohms. ?? The reading i got was 2.6 ohms ??

where are you getting the 1667 from ?

thanks
 
oh dear..
 
  • Like
Reactions: 9 people
My ZE reading was 187 ohms

So far so good,its after that you are losing the plot

Clue for research purposes only
Its a TT system with a 30 m/amp rcd

icon7.png


 
  • Like
Reactions: 1 person
Ok, so on page 50 on the regs, is states that the max ZS is 1667 for TT, so does page 103 of the OSG not contridict this ?

Sorry, but i am a bit confused......
 
Sorry and everything, but oh my god! You quite obviously don't really understand what your doing! If you had 180ohm odd as a Ze, then theres no way in hell your going to get 2.6 ohm Zs!! Zs will never be lower than Ze
 
  • Like
Reactions: 1 person
Hi srl-8 If you cannot get get your Zs down to meet disconnection you can employ an RCD but remember touch voltage 1667 x 30mA = <50V (Touch voltage).

Also remember disconnection in TT is less than a TN system i.e. 0.2s vs 0.4s - 411.3.2.2

Plus are the figures correct - remember Zs = Ze + (r1+r2) so Zs cannot be lower than Ze...
 
Last edited by a moderator:
Sorry and everything, but oh my god! You quite obviously don't really understand what your doing! If you had 180ohm odd as a Ze, then theres no way in hell your going to get 2.6 ohm Zs!! Zs will never be lower than Ze
yes it will, due to parallel paths via the bonding of gas and water. lead pipe is a bloody good earth.
 
  • Like
Reactions: 10 people
Sorry and everything, but oh my god! You quite obviously don't really understand what your doing! If you had 180ohm odd as a Ze, then theres no way in hell your going to get 2.6 ohm Zs!! Zs will never be lower than Ze


Sorry Richard, but I have to disagree with you. From my experience a ZS on a TT system is more often than not lower than the ZE. This is due to parallel paths through water and gas services.
 
  • Like
Reactions: 3 people
To be fair, the OP hasn't mentioned anything about bonding. But yes, i'd aggree that more often than not, a TT system with a lead water pipe will he significantly lower Zs's than the Ze.
 
Sorry Richard, but I have to disagree with you. From my experience a ZS on a TT system is more often than not lower than the ZE. This is due to parallel paths through water and gas services.
yep...at a house we were at recently.....Zs (at the board) through the gas and water services was in the region of 80 odd ohms....there was no earthing (rods or otherwise) to this installation other than what was being provided by the afore mentioned services.....
 
yep...at a house we were at recently.....Zs (at the board) through the gas and water services was in the region of 80 odd ohms....there was no earthing (rods or otherwise) to this installation other than what was being provided by the afore mentioned services.....

Yes, sorry I was trying to demonstrate a completly different point!! and completly aggree with wwhat you say!

Excluding Earth bonding for a second, the Zs cannot be lower than the Ze..correct? which I think the OP didn't understand.
 
assuming that BONDING not earth bonding..that dont exist mate......anyway assuming that main bonding conductors were not in place then a Zs should be higher than a Ze....but never forget the ability of parrallel paths to bring a measured value down....
 
agreed, but with bonding connected, your Ze effectively comes down from say 180 ohms to , in this case, around 2 0hms. this also means that the pefc will flow mostly through the bonding rather than the rod.
 
  • Like
Reactions: 2 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Very Hi ZS Reading on TT system? any advice
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
120
Unsolved
--

Advert

Thread statistics

Created
srl-8,
Last reply from
malcolmsanford,
Replies
120
Views
45,338

Advert