Hi this is my first time on this forum so take it easy please but I'm after a little bit of advice... I wonder if someone can help me calculate the voltage drop of an install that is in the process... I will give you as much info as possible, any help would be greatly appreciated...
.400a main intake head has been installed with a 400a isolator (3 phase 400v)
.Job is the install a sub main cable to feed an LV panel (400 supply)
.Sub main cable is SWA PVC 4core wired outside across a roof on perforated cable tray with a separate earth
.Cable run is 50m
I am trying to work out what size cable will be required and can't get to grips with the formula's, again any help would be appreciated.
Thanks Dan
assume that your max. allowable VD is 5%,
mV/A/m = (VD x 1000)/(L x A) . so once you have your mV figure, look up what cable size has that value.
Hi Dan. Welcome to the forum.
Am I understanding you post correctly? You want to feed a LV Panel that has a cable run of 50 meters and is protected by a 400A breaker?
400A cable is going to be big. It may be better running two cables in parallel.
Reply to Voltage Drop? in the UK Electrical Forum area at ElectriciansForums.net
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Hi There Just a quick one, I'm wondering what's everyone's thoughts on this are. A subby has clipped a cable to a plaster board ceiling using 3m...
Hi, We are working on a Solar installation in the UK and have been asked to replace the string cable terminations, 6mm² yellow insulated ring...
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...