Anyone know if the reduced height, switched neutral Wylex RCBO's will fit in this enclosure? Planning to rip the all the devices out and start again with all RCBO, but don't want to change the enclosure. I seem to remember the newer Wylex boards have a different shaped flap on the lid?

Maybe one for @westward10

IMG_9403.jpg
 
Why are you going to rip the board apart.
 
Why are you going to rip the board apart.
Wrong manufacturer fitted for a start. Also keeps randomly tripping despite rcd testing out ok and IR results good.

Guy is getting fed up as he works from home.
 
Wrong manufacturer fitted for a start. Also keeps randomly tripping despite rcd testing out ok and IR results good.
Me I would put a new lot in including the metal board if the client can afford it.
 
Me I would put a new lot in including the metal board if the client can afford it.
In this particular case it’s going to take a lot longer to do that as the board is bushed onto trunking in multiple places. There’s nothing wrong with the enclosure. It’s only about 3 years old.
 
Depends on the busbar.
The newer wylex miniture RCBOs only fit on the finger busbar as they don't have the slit in the front, also the busbar does have a kink in it where it connects to the L out of the main switch.
Trouble is the older Wylex busbar isn't as easy to get hold of, they do sell a AFDD busbar though.

Hager busbar is much easier to get hold of, you could change all the internals to Hager if changing the CU is going to be awkward.
 
I have Never seen PEP? before. What maker is this

Is that a Wylex RCD at the main switch ?
It’s a wylex enclosure and wylex rcd. Never seen PEP either.
 
Depends on the busbar.
The newer wylex miniture RCBOs only fit on the finger busbar as they don't have the slit in the front, also the busbar does have a kink in it where it connects to the L out of the main switch.
Trouble is the older Wylex busbar isn't as easy to get hold of, they do sell a AFDD busbar though.

Hager busbar is much easier to get hold of, you could change all the internals to Hager if changing the CU is going to be awkward.
Not sure if that would be permitted as it’s a wylex enclosure?

It’s very annoying how Wylex keep changing all the parts so they are not backwards compatible every 5 years or so. It’s mainly why I don’t use them!
 
I suppose I could rip it all out and start again with wylex finger busbar. Probably the best option.

The other problem if I fit Hager is will the front cover even line up over the devices?
 
It sounds like t he chap is frustrated with the tripping. I would just find the fault and fix it.
I'm assuming this isn't a wylex board otherwise you wouldn't be asking if it was compatible with wylex. In that case, you are swapping out one 'wrong' manufacturer for another wrong manufacturer.
I can understand it if the chap simply wants RCBO's to make future tripping less of a hassle though.

edit.. seen your other posts. I would probably take along all the bits needed in case you have to take everything out, but would try the wylex RCBO first in case it fits. Couldn't you use the older wylex RCBO's?
 
It sounds like t he chap is frustrated with the tripping. I would just find the fault and fix it.
I'm assuming this isn't a wylex board otherwise you wouldn't be asking if it was compatible with wylex. In that case, you are swapping out one 'wrong' manufacturer for another wrong manufacturer.
I can understand it if the chap simply wants RCBO's to make future tripping less of a hassle though.

edit.. seen your other posts. I would probably take along all the bits needed in case you have to take everything out, but would try the wylex RCBO first in case it fits. Couldn't you use the older wylex RCBO's?
There is no fault. It’s almost certainly an accumulation of earth leakage. I’d rather use the newer ones as they’re easier to work with!

I think I should be able to replace all the internals and pull the existing busbar out too. Then replace with new rcbos and new finger busbar.

I think the enclosure shown will have the busbar type that slots under the screw. Should’ve opened it up really ?‍♂️
 
  • Like
Reactions: HappyHippyDad
There is no fault. It’s almost certainly an accumulation of earth leakage. I’d rather use the newer ones as they’re easier to work with!

I think I should be able to replace all the internals and pull the existing busbar out too. Then replace with new rcbos and new finger busbar.

I think the enclosure shown will have the busbar type that slots under the screw. Should’ve opened it up really ?‍♂️
I've definitely started coming across this more over the past couple of years (i.e accumulated earth leakage tripping a dual RCD or single RCD board).
I was a bit behind everyone with singing the praises of RCBO boars, but I would say 95% of the time I fit RCBO boards now. The only time I fit the dual RCD is if the customer specifically chooses that due to cost.
 
If it has a "balcony style" (in Wylex parlance) bus bar, i.e. the one that fits under the screws rather than pokes up into the cage, then you might have a problem. Those with balcony bus bars only have half a DIN rail (the top half), when you place the protective devices into place the balcony bus bar is structural, keeping the bottom half of your devices fixed in place. So if you get all new devices and a new finger bus bar, then there's nothing to keep the bottom half of everything in place.

You could of course get the full height Wylex RCBOs, these are Type A, unfortunately they are not switched N, and I see it's a TT system so that may be your consideration.

Some of the more recent Wylex DB's - the "L" range (e.g. NM1106L) have a fixed, finger bus bar on the bottom and half a DIN rail, these are compatible with the newer devices. Unless the DB is one of these, or unless it's aleady got a finger bus bar of some sort, then you're out of luck.
 
  • Like
Reactions: pc1966
Think I’m going to open it up on Monday and have a proper look!
 
I like the way tt system is just randomly written on the cover. Great work
 
Having the PV system on the load side of other circuits' RCD protection is not good practice either! Is it that bank that keeps tripping by any chance?
 
  • Like
Reactions: suffolkspark
I agree with @suffolkspark that doesn't look like Wylex. The cover door looks too big, the embossed ON/OFF and CE mark is not a Wylex thing and the cover screws are off centre.
 
  • Like
Reactions: suffolkspark
Can't find any info on PEP but I would say the rogue component is the Wylex rcd which doesn't seem to sit correctly and probably replaced the original 60947-3 switch.
 
  • Like
Reactions: suffolkspark

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

mattg4321

Arms
~
Joined
Location
South East UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Wylex Compatibility
Prefix
N/A
Forum
Electrical Tools and Products
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
mattg4321,
Last reply from
Mike Johnson,
Replies
25
Views
8,288

Advert