It looks like you have 3 conductors on your supply cable, but who knows what is going on inside the cutout. You could try contacting your DNO to see if they have a record of the supply type to the property. ESQCR regulations require them to maintain the earth, if they are providing you with one.
Thanks for that
[automerge]1590494777[/automerge]
agree with all of above. looks like the cable coming up to the outside box is lead sheathed , the sheath being the TN-S earth. maybe a bad connection at that box or at cut-out.

can you see if you get similar readings at neighbours fed from same outside box?
It certainly does not look right! Can you confirm that your 2 lead / 3 lead tests were both done at the same location? If you repeat the test do you get the same results (i.e. did a high current check alter the low current reading)?

While going from high to low current can lead to a loss of accuracy at low-Z it is not going to explain more than a fraction of an ohm, same for "RCD uplift" which is usually 0.5 ohm or so and probably not an issue with newer MFT equipment anyway.

My suspicion is a bad connection on the earth line at CU/MET/DNO but you need to rule out the customer-side of the system (CU & MET) as a problem.

yes all at same location main earth disconnected, terminations sound. Test done 3 times. My company does not allow any tampering with DNO kit so we’ll have to pass it on. Cheers
[automerge]1590495284[/automerge]
99.99% that's TN, as has been suggested I would request a couple of quick tests done on neighbours properties to narrow down the problem and inform the DNO.

Take a look at page 24 of the attached, you could get the DNO out prety much straight away to sort this out.

MOCOPA-guide-version-3.5.pdf
Thank you for that I’ll have a read of that later. I assumed it was TN-S as there are 3 cables and looks like the armour is the making the 3rd cable but the reading made me question it.
 
Last edited:

Reply to Ze=1.87 TT or TN-S? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

....TN-S appears outside, butt TT employed inside. Good Evening Everybody (This is my first post) Overview: The supply to my parent's cottage...
Replies
29
Views
4K
Hello everyone, I know this has come upquite often, I have gone back through the many threads relating tothis topic. The reason for wanting to...
Replies
26
Views
15K
GEOFF S
G
Testing at a house today. The supply is a TN-S. Earth taken from lead incomer cable. First test with my Megger 1730 gave me Ze of 3.5 Ohms, way...
Replies
53
Views
5K
Hi I'm fairly new to the forum and have a situation I've never came across before. I visited a customers house to quote for a new consumer unit...
Replies
13
Views
4K
Engineer54
E
H
I am finding this quite a complicated subject, and I would really welcome your thoughts on this subject. If I could start with a TT system...
Replies
11
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top