scootknew

can someone please clarify this for me im at my wits end,

there are currently no plastic fuse boxes that are non cumbustible for sale from wholesales?

if fit a plastic cu, need to box it in with plaster board ect?

if i wire in new circuit from a new plastic cu to say a socket in hallway, i cant issue minor works cert? then its a fail? then say the client who wanted a £50 socket wired to hall needs to pay 100's to ge cu changed to metal? or enclose it? whos responsibility is it to enclose it? a joniner or builder? they will prob change a **** load too?

any info much appreacited
 
6862f3a448397766511964c7ac46780c.png
taken from the electrical safety 1st website.......although from your OP for a new circuit you should be issuing an EIC for a new circuit not a minor works.
 
Last edited by a moderator:
  • Like
Reactions: 1 person
can someone please clarify this for me im at my wits end,

there are currently no plastic fuse boxes that are non cumbustible for sale from wholesales?

if fit a plastic cu, need to box it in with plaster board ect?

if i wire in new circuit from a new plastic cu to say a socket in hallway, i cant issue minor works cert? then its a fail? then say the client who wanted a £50 socket wired to hall needs to pay 100's to ge cu changed to metal? or enclose it? whos responsibility is it to enclose it? a joniner or builder? they will prob change a **** load too?

any info much appreacited

Same as if the CU was metal. An EIC on the other hand!
 
can someone please clarify this for me im at my wits end,

there are currently no plastic fuse boxes that are non cumbustible for sale from wholesales?

if fit a plastic cu, need to box it in with plaster board ect?

if i wire in new circuit from a new plastic cu to say a socket in hallway, i cant issue minor works cert? then its a fail? then say the client who wanted a £50 socket wired to hall needs to pay 100's to ge cu changed to metal? or enclose it? whos responsibility is it to enclose it? a joniner or builder? they will prob change a **** load too?

any info much appreacited


What does a minor new works cert cover? certainly not a new circuit.
 
Last edited:
also my other question not been answered.

plastic cu non-combustible do they exisit i cant seem to find them?

so if i do eicr on a 1 bed flat for example, cu is plastic, i tell owner, put in plaster board box or change to metal? who puts it in plasterboard then?
 
also my other question not been answered.

plastic cu non-combustible do they exisit i cant seem to find them?

so if i do eicr on a 1 bed flat for example, cu is plastic, i tell owner, put in plaster board box or change to metal? who puts it in plasterboard then?

If you read the regulation it actually tells you the answer to this.
You code it with a suitable code and advise the customer accordingly. you do not 'tell owner' what to do, you advise.

What has plasterboard got to do with it?
 
so to my knowledge , there are no 17th edition am 3 "plastic" consumer units?

well see, plasterboard has 2 hour fire rating, so if not want to change cu to metal then need to put in enclosure as per regs. so i wud assume plasterboard is easyiest way?
 
so to my knowledge , there are no 17th edition am 3 "plastic" consumer units?

well see, plasterboard has 2 hour fire rating, so if not want to change cu to metal then need to put in enclosure as per regs. so i wud assume plasterboard is easyiest way?

30 minutes fire resistance usually for single board. And there is no need to enclose a CU in it.
 
Last edited by a moderator:
30 minutes fire resistance usually for single board. And there is no need to enclose a CU in it.

so what would u do if doing an eicr and came across a plastic cu? mark it as unsatifactory? well what if its rental flat ?
 
so what would u do if doing an eicr and came across a plastic cu? mark it as unsatifactory? well what if its rental flat ?

I would code it according to the guidance printed in my copy of the regulations, which I can't quote because it's in the van and I can't be bothered to go and get it. I think the answer is going to be no code though.

Codes are exactly the same for a rental flat as they are for any other installation.
 
  • Like
Reactions: 1 person
so to my knowledge , there are no 17th edition am 3 "plastic" consumer units?

well see, plasterboard has 2 hour fire rating, so if not want to change cu to metal then need to put in enclosure as per regs. so i wud assume plasterboard is easyiest way?

Different plaster boards have different fire ratings, but the regulations do not specify a fire rating for the enclosure, rather they specify a non combustible enclosure.
Fire rating and non combustible are two different things. A standard wooden door can have a 30min fire rating but it is sure as hell combustible.
 
  • Like
Reactions: 1 person
yeah but if eicr is unsatisfactory it means the flat cant be tenanted or let

No it doesn't, it means that the electrical installation has been found to be unsatisfactory when judged against the current diction of bs7671 (with allowance made for age of installation etc)

Why do you think that it has any effect on it being able to be let?
 

Similar threads

T
Replies
11
Views
2K
Australia
Engineer54
E
S
  • Question Question
Replies
2
Views
1K
Australia
SirKit Breaker
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
new cu changes 1st jan/16
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
110

Advert

Thread statistics

Created
scootknew,
Last reply from
muzza1,
Replies
110
Views
8,604

Advert