So should he of recommended the rewire? I'd rather not have that done if it's not essential. As we have hardwood flooring and laminate in all rooms. It would be an absolute nightmare!

If and I do say If you have rubber covered wiring & wiring with no earth conductors then yes, you need a rewire.
Please take the advice already given to you, by several of us & get a proper electrical contractor in to look at it.

That "Certificate" you've been given, really isn't worth the paper it's written on.
 
Are those the rubber wires he's referring to? The ones he advised to get the electricity board to replace (free of charge)

2017-06-17-13-44-44.jpg
 
Are those the rubber wires he's referring to? The ones he advised to get the electricity board to replace (free if charge)

View attachment 36877

They won't replace them they are after the meter. All they will do is put you an isolator in. I can't understand why your electrician who must of pulled the main fuse didn't connect straight into the meter??
 
They won't replace them they are after the meter. All they will do is put you an isolator in. I can't understand why your electrician who must of pulled the main fuse didn't connect straight into the meter??

Good question, especially as the meter seal seems to already have been cut.
 
So should he of recommended the rewire? I'd rather not have that done if it's not essential. As we have hardwood flooring and laminate in all rooms. It would be an absolute nightmare!

If what he has written is correct then in my opinion the replacement of the rubber cable in the cooker and lighting circuits should have been a higher priority than replacing the consumer unit.
personally I would refuse to carry out any work on your installation without first properly inspecting it and getting it agreed in writing that all such dangerous items will be fixed.
 
Thing is, when it's getting late at night, it sometimes difficult to remember which form to use. Suppose it saves on paperwork :)

OP, just curious about your new consumer unit, could you post a picture with the lid lifted up (one on a hinge)?

To verify if your electrician is in a scheme, you can try this link (think you said he was in NICEIC?);

Competent Persons Register | Home - http://www.competentperson.co.uk/

He should notify your local building control as well for the CU change, if he's in a scheme. If he's not in a scheme, its going to complicate things a bit. It is the home owners responsibility ultimately.
 
Thing is, when it's getting late at night, it sometimes difficult to remember which form to use. Suppose it saves on paperwork :)

OP, just curious about your new consumer unit, could you post a picture with the lid lifted up (one on a hinge)?

To verify if your electrician is in a scheme, you can try this link (think you said he was in NICEIC?);

Competent Persons Register | Home - http://www.competentperson.co.uk/

He should notify your local building control as well for the CU change, if he's in a scheme. If he's not in a scheme, its going to complicate things a bit. It is the home owners responsibility ultimately.


I see 1 company name that matches on there, but isn't anywhere near where I live?
 
Pete, ya gotta explain that one to me sometime mate ;)
Nothing to explain in all honesty, I'm not the person to claim the cudos from someone else, it was a member of the forum who first introduced me to this description (Kennyken) get the feeling it may be the Australian equivalent of the ubiquitous Electrical Trainee anyway I like it better, thanks Kenny for the pleasure it has given me, I think it's a cracker of a phrase sort of runs off of your tounge "Boil in the Bag Sparkie" wonderful:);):p:rolleyes:nice one kenny
 
Where are these rubber wires located for the cooker and lighting? Inside the CU? Sorry I'm no electrician. :)

If they are at the fusebox then they would go from there to whatever circuit they serve i.e within walls, under floorboards etc.
Without actually seeing the installation we have no way of knowing exactly where.
 
If they are at the fusebox then they would go from there to whatever circuit they serve i.e within walls, under floorboards etc.
Without actually seeing the installation we have no way of knowing exactly where.


I've seen under the floor boards before, and they are all grey pvc cables... How did the guy know they are rubber if he hasn't even looked??
 
Nothing to explain in all honesty, I'm not the person to claim the cudos from someone else, it was a member of the forum who first introduced me to this description (Kennyken) get the feeling it may be the Australian equivalent of the ubiquitous Electrical Trainee anyway I like it better, thanks Kenny for the pleasure it has given me, I think it's a cracker of a phrase sort of runs off of your tounge "Boil in the Bag Sparkie" wonderful:);):p:rolleyes:nice one kenny

Agreed, it's a brilliant saying. Talking of Kenny, any idea where he's dissapeared to ?.
 
I see 1 company name that matches on there, but isn't anywhere near where I live?

You should contact the NICEIC without delay regarding this cert. If this chancer is not an approved contractor and using their logo they will pursue him and take legal action.
If guilty he will pay a hefty fine, if he is approved you have a justifiable claim against his work and incorrect certification.
 
So the cable inside the walls? The only visible cables I can see are all PVC... The cable the cooker is attached to is Grey PVC...

As the others have said, its difficult to tell from this side of a PC screen. As this electrician has not completed the correct certificate for a CU change, amongst other things. I would see if another electrician/company could check this change and advise you accordingly.

You could phone NICEIC on Monday, to verify if this electrician is registered with them. It does appear, from the photos you've posted, not to be a satisfactory situation.

If he is with NICEIC, and things have been incorrectly installed, NICEIC will say that the electrician should be given the opportunity to put things right. Personally, I would not let him back in my house.
 
I've seen under the floor boards before, and they are all grey pvc cables... How did the guy know they are rubber if he hasn't even looked??

OK sorry I'm done with this now, it's already turned into a 10 page farce. You've been given good advice by professional electrician's, your choice whether you take it or not.
 
Unfortunately your right & it's getting worse.
I don't know if you, Andy, or anyone else bothers to check the Profile of posters I don't know, I do, we have all heard and spoken a lot about young inexperienced Electricians, understandable, we, all of us had to learn and gain knowledge from experience, qualifications are a good and necessary thing, the one thing that ticks me off no end, is people who think they are Electricians, but perhaps would be better off doing something else, the descriptions on some of the profiles, "what electrical qualifications do you hold" some people don't bother for one reason or another, but some add things like "all of them" or "enough" makes my blood boil. The only reason I check is to tailor my answers, not to gloat I just feel lucky to have done an Apprenticeship, sorry for the rant Guys and Gals.
 
I don't know if you, Andy, or anyone else bothers to check the Profile of posters I don't know, I do, we have all heard and spoken a lot about young inexperienced Electricians, understandable, we, all of us had to learn and gain knowledge from experience, qualifications are a good and necessary thing, the one thing that ticks me off no end, is people who think they are Electricians, but perhaps would be better off doing something else, the descriptions on some of the profiles, "what electrical qualifications do you hold" some people don't bother for one reason or another, but some add things like "all of them" or "enough" makes my blood boil. The only reason I check is to tailor my answers, not to gloat I just feel lucky to have done an Apprenticeship, sorry for the rant Guys and Gals.

I do sometimes check them yes Pete, but then I think why bother. I could alter my profile to say I had a Degree instead of C & G etc & no one would actually know the difference.

Actually: Thanks Pete, you just reminded me. I haven't seen my folder since we moved here.
 
Another departure from the wiring regs OP. There should be two RCD's to give division of installation. Something easily achieved.

I would recommend you have this CU change and the remainder of the installation checked by another electrician/company.

Let us know what NICEIC say.
 
So the cable inside the walls? The only visible cables I can see are all PVC... The cable the cooker is attached to is Grey PVC...

In the past cables have been manufactured with rubber insulation and grey sheath, the sheath wasn't always PVC either.

How do you expect us to know where he saw these cables? Why don't you just ask him?
 
In the past cables have been manufactured with rubber insulation and grey sheath, the sheath wasn't always PVC either.

How do you expect us to know where he saw these cables? Why don't you just ask him?

Calm down dude. Was just asking... I'm not an electrician I know nothing. Seems the "electrician" knows nothing either. I'll see what niceic have to say.
 
Calm down dude. Was just asking... I'm not an electrician I know nothing. Seems the "electrician" knows nothing either. I'll see what niceic have to say.

Don't mind davesparks, he's very knowledgeable about electric's, learnt quite a bit from him myself. In return, I've been trying to learn him the art of diplomacy. He has improved in recent times :)
 
I'm guessing this happens a lot, cowboy electricians doing botched jobs. While the customer remains totally oblivious and assumes all is up to standard.

I hope you intend to follow this up. As said before, from your descriptions and photos, there appear to be some questions to be asked. Firstly, it would be interesting as to what NICEIC say, if this electrician is registered with them. A lot of the chaps on here have a poor view of schemes, but lets see.
 

Reply to Smoke coming from electric meter/fuse box area in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
675
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K
Hi all, I am an experienced DIY electrician and I just wanted to ask a quick question about something since I am new to this forum, if it hasn’t...
Replies
11
Views
2K
Hello all, I need to have an electric car charger installed but at the moment I'm puzzled about what my options are. My garage is at the back of...
Replies
4
Views
701
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
865

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock