I would say that all the members on here love their job and the challenges it brings. Once the understanding is there everything falls into place , the more understanding you get the easier it gets and the more you want to know......
 
I think you were correct. Ignoring the regs and requirements,for a minute,the tests to check the supply characteristics,are not onerous or particularly time consuming.

They can,on occasion,flag up issues,and lead us in other directions,sometimes directly concerned with safety,which is a primary reason for most of our governance.

I would hazard a guess,that the others on your course,giving you a hard time,were probably older,maybe considering themselves to have so much more experience,these tasks were unnecessary. They are wrong.

We can all shoe,a dead horse. It is probably easier.
But sooner or later,when we stick our hand out for payment,someone is going to ask if we checked...
 
  • Like
Reactions: ruston
Had almost this situation in real life. Went to do an addition. Checked EFLI before starting and they’d lost their earth due to corrosion of conductors on the pole outside. DNO came straight out and fixed it.
 
Top job well done.
 
  • Agree
  • Like
Reactions: ruston and gazdkw82
Earth fault loop impedance revision of ENA Engineering Recommendation P23 - https://electrical.----------/wiring-matters/issues/72/earth-fault-loop-impedance-revision-of-ena-engineering-recommendation-p23/ This is an interesting read for max Ze values probably one of the few places you will find it recorded, Engineers Recommendation P23/2:2018.
 
  • Like
Reactions: gazdkw82
Well done firstly

How and in what way was it difficult?

Understanding what the question is truly asking if the biggest challenge. Once you break the questions down it's usually simple but the questions are really tricky.

For example I had one that said something along the lines of "a 30ma RCD was tested at 150ma and found to trip at 500ma. What would this indicate"

Possible answers were,

A. The rcd provides efficient fault current protection

B. The rcd will be subject to noisance tripping

C. The rcd test button has been regularly checked

D. (Something along the lines of) the rcd is working perfectly.

It had me guessing because it's not obvious.

Some of the questions were difficult to find or work out. For example, if a earth electrode has a resistance of 27ohms, what would be the maximum rated rcd allowable on the installation....

Just a few examples. I can remember quitr a few but I'd be here all night.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

gazdkw82

Arms
~
Joined
Location
leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Pre site inspection 2391-52 scenario
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
gazdkw82,
Last reply from
gazdkw82,
Replies
28
Views
401

Advert