T
Themorganator4
Hi there,
I have an air source heat pump with a few issues:
1. It gets stuck on defrost mode. When it goes to defrost, it gets stuck and ends up becoming an air conditioner in the depths of winter (fun). I suspect this may be a faulty valve (or what ever reverses the coolant) getting stuck on reverse. I have disabled defrost mode for now by disconnecting the relevant module (bodge fix I know but it's that or I freeze and have no hot water)
2. When the programmer demands heating the pump doesn't kick into action, I have to run the hot water for a bit (to demand hot water) and the pump kicks into action for both heating and hot water, once the hot water reaches temp it shuts off even if heating is still being demanded.
I know there is no issue with the heating system in the house as the rads heat up as normal when the heat pump is on, it's just that it doesn't come on when I demand heating only.
So somewhere there is a link between the programmer and the heat pump broken so the pump doesn't know when heating is being demanded.
What do you guys think I should do? Where should I test?
Hi - can I ask how old is the system and when did it stop working properly? What electrical test kit have you got?
It's about 5 years old and it has never worked correctly. We moved in to the property this summer so the defrost and heating issue wernt apparent.
I have a multi meter.
Hi there,
Can I ask the make? Note not the seller but the company that made it.
Point one is either a parameter issue or a sensor is reading wrong, become detached or has always been in the wrong position.
A heat pump relies on a combination of sensors to function and many sensors have multiple uses.
So one faulty sensor could be the cause of all your problems.
If you can run the HP without the defrost mode without it turning into a block of ice then it shouldn't do it any harm.
Be very observant for ice build up, if it gets thick enough to touch the fans it's goodnight Vienna.
If it is going into defrost without a meaningful amount of ice on the coil then the onset temperature is to high and it will be costing you money.
Very few people get an efficient and reliable heat pump using the out of the box setting. Many areas have their own micro climate and require different settings.
On point two, the module you've removed may have stopped the physical action of the HP defrosting but the program may still think it is defrosting thus not allowing heating.
Do you have a parameter table?
Can you work the controller, the thing on the wall inside?
If so yo can see what each sensor if reading and sanity check it.
EG the ambient sensor could have faulted giving a default -20C reading, if the defrost onset is set at -2C then it will spend a lot of time defrosting.
or the Evaporator Coil exit sensor could be goosed, reading -20C and, depending on the defrost program, it will never come out of defrost.
Just noticed the manual you linked.
As it doesn't give any info on default parameters or controller operation its pretty useless.
the only thing I know for sure is it's not a China Palm, a very good thing.
Thanks for your reply, it is an ideal airtherm 4.5 and by the controller do you mean the programmer where you set the time for the hot water etc or a controller in the heat pump itself?
I should also mention that the heat pump has never kicked into action when heating is turned on, regardless if the pump is in defrost or not (I have a light which illuminates on defrost) only when hot water is called for.
I've had a quick google and can find no info on this maker or model of any use.
All HPs are different but there must be a way to view the various sensors and parameters.
It may be worth giving Ideal a ring, this sounds like the kind of issue that can be solved over the phone IF you have access to to the engineers manual.
It sounds like it has never been fully commissioned.
A lot of people bought heat pumps and got their local plumber to install them, often they get the mechanics right but totally fail to set the thing up correctly.
Hi - if I understand correctly the HW works and you can use it to get heating running. Are you familiar with S plan systems with two 2 port valves, is that how the ASHP is plumbed (?).
I'm not familiar with s plan systems or 2 port valves. I'm a bit of a noob when it comes to this stuff
Hi Morgan - for me the next steps would likely be to look at the control system and then the ASHP itself. Sorry to say, but I think you're going to need on site help with this fault.
Just had a look at 2 port valves. Is it possible that the heating valve is faulty? I.e it opens and closes but doesn't signal to the heat pump that it is open so therefore the pump doesn't operate?
I was hoping you wouldn't say that, I had the company out last year and they charged me about 500 quid to replace the defrost module (which didn't fix the problem) they then wanted to replace the smart starter, it seemed that they were just replacing random parts hoping it would fix the problem, charging me for the pleasure. I eventually told them enough was enough and I was not paying them any more.
That is correct, I believe it is an s plan system with 2 port valves
After educating myself with an s plan system etc, would it be a good idea to check the heating valve is sending the signal to the heat pump to say it is open and therefore turning on heating? As the valve opens (hence the heating working under hot water) but may not be telling the heat pump this.
Hi - I think you've got a control system problem and an ASHP problem.
My best guess is the orange wire from the zone valve is not being made L so the ASHP doesn't know to make heat. If you go near those zone valves be aware there are 240V connections - Danger Morgan, Danger. Several faults can have the same effect (cabling, microswitch, motor for example). An experienced Electrician should confirm if the fault is there fairly quickly, just saying. After the control system is working properly that will still leave the defrost problem, sorry.
Don't worry, I may not have much experience in electrics but I know how to isolate a system and not touch live wires haha.
Frankly I don't care about the defrost issue currently as it never ices up much. As long as I get heat on demand then I'm happy
Hi - no no no, maybe :).
Power may not be coming into valve on the the grey wire. Or the connection from the orange to the boiler may be no more etc ...
So the orange is the wire which tells the ASHP the valve is open and to make heat and that's what you suspect is the issue?
Are you also saying if that wire is not live then it doesn't necessarily mean the valve is faulty?
Luckily I have a friend who is a plumber and he may have a spare valve motor we can try just to see if that is the problem
Also one of the valves has the switch stuck on manual (it has been jammed for some reason) would that cause this issue. I forgot to mentiin this earlier! Sorry.
Check which valve is stuck :)
As in hot water or heating? If it's the heating valve then id imagine that's the problem and it will just be a case of moving it to auto (if I can free it) or getting a new valve motor
Before I check the orange wire with a multi meter, I'm looking for 250v on this wire when the heating is on and 0v when heating off right?
Ok so how would I test it to see if it is faulty? Measure resistance?
A voltage tester which doesn't give false readings due to phantom voltages would be my choice of tester for this. You could try the multimeter, but there's no guarantee that the results you get will. Be correct unfortunately.
Right, before you start pulling things to bits you need to check whether there is power at terminal 9 of the heat pump wiring centre, see page 9 of the manual.
If you have 230 at terminal 9 then the HP is asking the MV to open, if there is no power then the HP is not asking for heating regardless of what the controller says.
I still think this is a parameter error or sensor fault.
If you have power at terminal 9 and no power at the MV then a broken wire you have, or a hidden JB.
The ones I've seen tend to power the MVs from the HP, the orange/grey being used to power pumps via contactors.
Is there and internal wiring centre? If so a loose connection in there may be the cause.
Air source heat pump heating issue
Central Heating Systems
Themorganator4,
Themorganator4,