Hi - I think you've got a control system problem and an ASHP problem.
My best guess is the orange wire from the zone valve is not being made L so the ASHP doesn't know to make heat. If you go near those zone valves be aware there are 240V connections - Danger Morgan, Danger. Several faults can have the same effect (cabling, microswitch, motor for example). An experienced Electrician should confirm if the fault is there fairly quickly, just saying. After the control system is working properly that will still leave the defrost problem, sorry.

Don't worry, I may not have much experience in electrics but I know how to isolate a system and not touch live wires haha.

Frankly I don't care about the defrost issue currently as it never ices up much. As long as I get heat on demand then I'm happy
 
Hi - no no no, maybe :).
Power may not be coming into valve on the the grey wire. Or the connection from the orange to the boiler may be no more etc ...
 
Hi - no no no, maybe :).
Power may not be coming into valve on the the grey wire. Or the connection from the orange to the boiler may be no more etc ...
So the orange is the wire which tells the ASHP the valve is open and to make heat and that's what you suspect is the issue?

Are you also saying if that wire is not live then it doesn't necessarily mean the valve is faulty?
 
Right, before you start pulling things to bits you need to check whether there is power at terminal 9 of the heat pump wiring centre, see page 9 of the manual.

If you have 230 at terminal 9 then the HP is asking the MV to open, if there is no power then the HP is not asking for heating regardless of what the controller says.

I still think this is a parameter error or sensor fault.

If you have power at terminal 9 and no power at the MV then a broken wire you have, or a hidden JB.

The ones I've seen tend to power the MVs from the HP, the orange/grey being used to power pumps via contactors.

Is there and internal wiring centre? If so a loose connection in there may be the cause.
 

Reply to Air source heat pump heating issue in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi all, I've noticed that my UFH pump is not always turning on as soon as the stat & valve calls for heat. This results in hot water passing...
Replies
8
Views
604
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
890
Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
Replies
5
Views
951
Hello , I’m trying to further my knowledge into UFH/Rad/HW valves heating systems with air source pumps. What is normally needed outside with...
Replies
0
Views
577
Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock