you could check to see if the fault is on the live by doing an R1. We're assuming here the fault is on the earth, but that is only one half of the story given the tests conducted?
 
yea i'll give that a go, but would the CSA of the conduit have anything to do with it? or would that normally make the readings alot lower yea? is that right?
 
Is the conduit earthed correctly at the consumer unit? Does the consumer unit connect into the conduit? is the consumer unit plastic by any chance? Are all the other circuits earthed using the same wiring method?

we are all sat at home in front of keyboards with a beer cos nothing is on TV.

We need the maximum amount of info if we are to help.

AND, when you do get it sorted, come back on here and tell us what the problem was so we can all learn!
 
yea i'll give that a go, but would the CSA of the conduit have anything to do with it? or would that normally make the readings alot lower yea? is that right?

Conduit earthing would normally make it lower, unless there is a plastic section in it! Or is it all plastic?
 
even the dis board?

Take a wander lead from MET to all accessible points and see where breakdown or errant readings start.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Very high r1+r2 readings and Zs in conduit?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
Kev2632,
Last reply from
VoltzElectrical,
Replies
25
Views
3,961

Advert