CU job for a customer on a bit of a budget so little room for alterations.

Part of the job, I find a small single garage conversion to ground floor bedroom (ie a small room), converted in 1980’s. Found to have it's four sockets supplied via 1.5mm ring.

Anyhow, reconnecting into new CU, I measure a low insulation resistance on one jump of the ring. I have isolated that part, and converted remaining circuit into two radials, (IR measures up OK now), still using the existing 1.5mm, and fitted new CU with 10A MCB with label “10A Max”, and will also note it in EIC. Customer will never require much current in there since it's bedside lamps and a computer, and it's only the one little room.

Does a radial to sockets on 10A MCB in 1.5mm classify as “Departure form BS7871” as far as EIC is concerned? I can’t find anything which specifically says this can’t be done. I will be recording ref method A for the ex cables, hence 10A max.
 
im gonna jump in with its fine before all the hand-wringers turn up lol.
and because the EIC only covers your work , not the existing wiring , no need to record as a departure
;-)
 
Whilst not a standard circuit, if it is safe and complies with the regs, then I can`t see an issue. 1.5mm2 is the minimum for power circuits. It is not a departure unless you can find a reason for it not being compliant.
 
the departures section only covers the parts of your own work that has been designed / selected with methods outside bs7671 , its not to record defects already present.
 
Need to know reference method and approx length of the 1.5 and is it a single or twin socket on the end of the 1.5mm.

What im getting at here is if its in a stud wall in insulation and not touching either surface then this set-up can be a fire hazard although as you state its an old conversion and unlikely to be this method in the eighties.
 
Last edited:
I am going from memory here, but ccc of 1.5mm is 19.5amps ref. method C so even if this is halved it would be fine if in insulation, bearing in mind it is wired as a ring and is on a 10amp breaker. Don't know if I need it but, tin hat on just in case.

Edit: Just re-read OP and seen he has split the ring into two radials. Ignore what I just posted! Would not be OK in insulation.

P.S. Dont drink and post.
 
Yes just had a thought ref method 103 would make it 10amps now with a 10amp mcb on it it is possible to put a small overload on the circuit for a long duration... should never assume its only going to have small items plugged in what if the boiler failed and they plugged in a 3kw heater in at approx 13amps which is less then 1.45x mcb rating and below its trip threshold on overload.
Now dont we have a reg' that says all circuits should be designed to ensure a small overload is not likely for a long duration.

Yes probably not an issue for the OP but food for thought next time he comes across this set-up and as he has altered the circuit he becomes responsible for it.
 
Hi Andrew,
The wiring was DIY'd in the 1980's. I found a kitchen sockets wired as an interesting set of branching spurs also in 1.5. - Also needs to be got rid of as soon as the owner clears the place out.
The kitchen is genuinely ref method C, so I downgraded it to 16A. (The garage conversion was conduited in foam insulation, somewhere between 102 and A, hence 10A).
 
CU job for a customer on a bit of a budget so little room for alterations.

Part of the job, I find a small single garage conversion to ground floor bedroom (ie a small room), converted in 1980’s. Found to have it's four sockets supplied via 1.5mm ring.

Anyhow, reconnecting into new CU, I measure a low insulation resistance on one jump of the ring. I have isolated that part, and converted remaining circuit into two radials, (IR measures up OK now), still using the existing 1.5mm, and fitted new CU with 10A MCB with label “10A Max”, and will also note it in EIC. Customer will never require much current in there since it's bedside lamps and a computer, and it's only the one little room.

Does a radial to sockets on 10A MCB in 1.5mm classify as “Departure form BS7871” as far as EIC is concerned? I can’t find anything which specifically says this can’t be done. I will be recording ref method A for the ex cables, hence 10A max.

In essence OK so long as the circuit protective conductor is at least a 1.0mm², and is the circuit afforded the additional protection of an RCD? I would suggest you take a read of Reg 433.1 and Chapter 15 of BS7671 as these are the sections that cover radials and rings from memory.
 

Reply to 10A MCB for 1.5mm radial to sockets? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
619
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Locked
We have a garage attached to the property and are having it converted to an office with a small toilet. Electrics will include, internal lights...
Replies
35
Views
5K
Hi everyone. I need a little advice please. Several months ago I first fixed and second fixed a timber frame loft conversion ( open plan living...
Replies
18
Views
4K
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock