Hi All

We are designing a G83 10kwp pv system to go on a 3 phase supply, using an SMA Tripower 10000TL. When calculating max AC amps will it be calculated at 10000 / 415v = 24/25 amps? We are looking to install one 4 pole AC isolator.

Also what size tp mcb is is best to install.

Thanks
 
Hi All

We are designing a G83 10kwp pv system to go on a 3 phase supply, using an SMA Tripower 10000TL. When calculating max AC amps will it be calculated at 10000 / 415v = 24/25 amps? We are looking to install one 4 pole AC isolator.

Thanks

Thats not the way to calculate 3 phase currents. Assuming balanced

Current = Power/3/voltage
So in you case
10000/3/230 = 14.5A

Sanity check 3.68kW on 1 ph = 16A
3 x 3.68kW = 11.04kw @ 16A /phase
 
Cheers for the reply

So a 16a tp mcb will be suitable on this install then?

UK Power Networks are the DNO here and up until recently they had been advising 3.84kw @ 240v =16amp was ok, which after speaking to them a week ago appear to have moved in line with other DNO's and dropped to 3.68kw per phase.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3 phase 10kwp system
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
bigsparks,
Last reply from
bigsparks,
Replies
2
Views
1,757

Advert