Discuss 3 phase 10kwp system in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

B

bigsparks

Hi All

We are designing a G83 10kwp pv system to go on a 3 phase supply, using an SMA Tripower 10000TL. When calculating max AC amps will it be calculated at 10000 / 415v = 24/25 amps? We are looking to install one 4 pole AC isolator.

Also what size tp mcb is is best to install.

Thanks
 
Hi All

We are designing a G83 10kwp pv system to go on a 3 phase supply, using an SMA Tripower 10000TL. When calculating max AC amps will it be calculated at 10000 / 415v = 24/25 amps? We are looking to install one 4 pole AC isolator.

Thanks

Thats not the way to calculate 3 phase currents. Assuming balanced

Current = Power/3/voltage
So in you case
10000/3/230 = 14.5A

Sanity check 3.68kW on 1 ph = 16A
3 x 3.68kW = 11.04kw @ 16A /phase
 
Cheers for the reply

So a 16a tp mcb will be suitable on this install then?

UK Power Networks are the DNO here and up until recently they had been advising 3.84kw @ 240v =16amp was ok, which after speaking to them a week ago appear to have moved in line with other DNO's and dropped to 3.68kw per phase.
 

Reply to 3 phase 10kwp system in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
705
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
965
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
814
For power outages, my solar inverter (+battery) is able to take on the entire house load - as long as I unplug my collection of vintage kettles...
Replies
3
Views
837
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock