11kv/440-750kva 3 phase tx on 200A primary fuses, spotted this at work, whats the max current per phase you can draw on the secondary without rupturing the fuses.
750KVA @ 11KV = 39.3A.
Giving a bit of leeway for inrush and available fuse sizes 60A is what I would fit.
Now comes the BIG question, how do you know what size fuses are fitted? Have you looked in the switch?
I’m going to take a guess, you been looking at something like this
![]()
And seen this
![]()
Don’t interfere with things you don’t understand.
750KVA @ 11KV = 39.3A.
Giving a bit of leeway for inrush and available fuse sizes 60A is what I would fit.
Now comes the BIG question, how do you know what size fuses are fitted? Have you looked in the switch?
I’m going to take a guess, you been looking at something like this
![]()
And seen this
![]()
Don’t interfere with things you don’t understand.
Especially when there's a 'TYKE IIA' involved