Richard3009

11kv/440-750kva 3 phase tx on 200A primary fuses, spotted this at work, whats the max current per phase you can draw on the secondary without rupturing the fuses.
 
Enough to set the transformer on fire, yes. Is this a trick question?
 
I'd hazard a guess that it probably won't be possible to draw enough current from the secondary to blow those fuses due to the windings melting first. This is based purely on the primary/secondary ratio being 1:25 so to see 200A on the primary you'd need 5000A on teh secondary which is going to equate to a couple of MVA.
Which is a ridiculously rough estimate as it makes no allowance for losses or efficiency or power factor or anything else I don't even know about.

But my knowledge of those kind of transformers doesn't extend past being able to point one out in a substation so I wouldn't trust my word on it!
 
I'd call that a fairly accurate rough estimate. You could probably blow the fuses if you were quick about it though.
 
Well I was assuming that the primary fuses wouldn't be the fastest acting fuses in the world, just using a bit of common sense (although I think that's been banned by the EU recently)
 
750KVA @ 11KV = 39.3A.

Giving a bit of leeway for inrush and available fuse sizes 60A is what I would fit.

Now comes the BIG question, how do you know what size fuses are fitted? Have you looked in the switch?

I’m going to take a guess, you been looking at something like this

IMG_0017_zps27bc0854.jpg


And seen this

IMG_0012C_zps8054228b.jpg


Don’t interfere with things you don’t understand.
 
Unlike some of the Long and Crawford gear. That sometimes has been found to explode when switched live!
 
Last edited by a moderator:
Ooo, nasty!
We used Long & Crawford on 3.3 as isolators, never switched live.

That Yorkshire gear was OK once:
The oil leaks were fixed.
The trip bar pivots replaced.
The trip latch replaced.
There were other faults, I’ve still got the report somewhere.
 
There's an embargo on a few models of the long and Crawford gear. Almost exclusively to the models fitted with striker fuses.

Most of the gear they built was actually top notch.
 
750KVA @ 11KV = 39.3A.

Giving a bit of leeway for inrush and available fuse sizes 60A is what I would fit.

Now comes the BIG question, how do you know what size fuses are fitted? Have you looked in the switch?

I’m going to take a guess, you been looking at something like this

IMG_0017_zps27bc0854.jpg


And seen this

IMG_0012C_zps8054228b.jpg


Don’t interfere with things you don’t understand.

I simply looked at the drawing of the circuit in the substation
 
750KVA @ 11KV = 39.3A.

Giving a bit of leeway for inrush and available fuse sizes 60A is what I would fit.

Now comes the BIG question, how do you know what size fuses are fitted? Have you looked in the switch?

I’m going to take a guess, you been looking at something like this

IMG_0017_zps27bc0854.jpg


And seen this

IMG_0012C_zps8054228b.jpg


Don’t interfere with things you don’t understand.

Especially when there's a 'TYKE IIA' involved
 

Reply to 750kva on 200A primary fuses in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
996
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
As per normal I was in a rush and didn't get enough information. I was working in an apartment that didn't have any power and when I went to...
Replies
8
Views
1K
Hi there im in training, but my question is using using a 3 phase 480v delta to 208/120 delta transformer 30kva and wiring it in reverse for 208...
Replies
1
Views
714

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock