As I inferred previously you need to establish whether the application that you are providing the VSD for is a variable torque or a constant torque one.
If it is variable torque then normally the size of the VSD equates to the same size of the motor eg 15kW pump, 15kW VSD.
If it's a constant torque application such as you appear to have then the VSD drive tends to be larger than the motor drive i.e. the larger VSD is derated (usually by the manufacturer) for constant torque applications.
Typical variable torque applications are centrifugal pumps, fans, blowers etc.
Typical constant torque applications are conveyors, positive displacement pumps, agitators etc.
It is a centrifugal pump so i have went down a model to 15Kw Vsd to suit 15KW motor. That clears things up thank a lot mate.