I am heading off next week to visit my parents (84 and 83). They live in a nicely decorated and carpeted 3 bed semi with original wiring from 1965.

I noticed last time I visited they have the dreaded green goo in the 7/029 wiring. The 1/044 lighting does not have it. They only have one or two single un-switched sockets in each room apart from kitchen and side extension which are all new and on separate circuits to the original sockets.

The advice I am seeking is on a good, neat, easy to install surface conduit system to contain wiring for new radials/rings upstairs and downstairs in the 3 bedrooms, hall, landing, lounge and dining room. I can then present it to my father and explain the benefits and ease of installation. Neither would cope with floorboards being lifted and walls chased. He is a chemist and read what it says about green goo so I don't need to convince him it's time to re-wire and at the same time to add more handy sockets higher up.
 
Last edited:
  • Like
Reactions: DPG
I am heading off next week to visit my parents (84 and 83). They live in a nicely decorated and carpeted 3 bed semi with original wiring from 1965.

But wouldn't surface trunking/conduit make the place look tacky/nasty???
 
  • Like
Reactions: DavidSpark
I am heading off next week to visit my parents (84 and 83). They live in a nicely decorated and carpeted 3 bed semi with original wiring from 1965.

I noticed last time I visited they have the dreaded green goo in the 7/029 wiring. The 1/044 lighting does not have it. They only have one or two single un-switched sockets in each room apart from kitchen and side extension which are all new and on separate circuits to the original sockets.

The advice I am seeking is on a good, neat, easy to install surface conduit system to contain wiring for new radials/rings upstairs and downstairs in the 3 bedrooms, hall, landing, lounge and dining room. I can then present it to my father and explain the benefits and ease of installation. Neither would cope with floorboards being lifted and walls chased. He is a chemist and read what it says about green goo so I don't need to convince him it's time to re-wire and at the same time to add more handy sockets higher up.
Difficult to say Mate without eyes on the house, my choice would be PVC trunking, but as Spoon said it will not look nice in a domestic setting, but definitely trunking over tube any day, where do they live?
 
  • Informative
  • Like
Reactions: marconi and Wilko
There's some nice rounded trunking available these days. Looks much better than the standard stuff.
 
  • Informative
Reactions: marconi
I remember years ago, we rewired some flats that had concrete ceilings. We used cornice trunking....
IMG_0005.JPG

....although we chased the wall upto the top, then fed cables through back of trunking, but as shown you can get adaptors for drops to points.
 
We fitted a load of MK coving trunking, hated it a lot.

How about surface bare MI? Unobtrusive, won't collapse in a fire or produce toxic smoke like plastic conduit and trunking does, fun to install etc.
 
Use mini trunking and wire atop skirting boards wherever possible.
 
  • Like
Reactions: marconi
Given the age of your parents it may be worth thinking about just living with it if test results are satisfactory. In my experience it rarely causes any real problems. New accessories if contaminated, and a clean up might be enough to nullify the problem for the time being. A surface rewire will be a short term solution in reality and will always look cheap however it's done.
 
Your chemist father doubtless understands the nastiness of the Dioctyl Phthalate, but a surface rewire will leave all that in place anyhow won't it?
If it's dripping out of the fittings (that does happen) I can understand the point, but though the cables get soft and a bit vulnerable in the areas it collects (bottoms of vertical runs mostly), in my experience they don't fail IR.
- Wear gloves and don't handle it!
 
How are the cables installed at the moment? I know most installs from around that era in my area would have been in oval or round steel conduit
 
Wait, just because you have the green stuff, does not necessary need to rewire, my suggestion would be wipe it off and IR the circuits. 7/029 pvc is better than the cable today. (I take it its copper)
 
Given the age of your parents it may be worth thinking about just living with it if test results are satisfactory. In my experience it rarely causes any real problems. New accessories if contaminated, and a clean up might be enough to nullify the problem for the time being. A surface rewire will be a short term solution in reality and will always look cheap however it's done.

So if after some FRC testing including IR the readings are satisfactory, one could keep the cabling (for my parents remaining lifetime) and renew the accessories. Could you tell me a little more about how this might be done please? Do you have to cut back the cable, splice on new tails and then connect these into the new accessories? Is there a best way of doing it? Afterwards, would one have to do regular FRC testing to check for any deterioration?
 
How are the cables installed at the moment? I know most installs from around that era in my area would have been in oval or round steel conduit

A loop around the first floor and then drops down from first floor sockets to the sockets immediately below on the ground floor. Drops in metal conduit. First floor threaded under the floor boards. Copper 7/029.
 
So if after some FRC testing including IR the readings are satisfactory, one could keep the cabling (for my parents remaining lifetime) and renew the accessories. Could you tell me a little more about how this might be done please? Do you have to cut back the cable, splice on new tails and then connect these into the new accessories? Is there a best way of doing it? Afterwards, would one have to do regular FRC testing to check for any deterioration?
As 7029Dave said it could be after testing that the cables are OK.
Changing accessories shouldn't be that arduous, you could change the single sockets for doubles, surface or flush, your choice on that issue.
You might like to think about a CU change with RCBOs, your elderly Parents have lived with these issues for a while, whilst I'm not discounting the safety issue, it would be a bit of an upheaval to put them through the trauma of a rewire at their age, not saying it shouldn't be considered, but there are things you can do to improve their twilight years, good luck whatever you decide.
 
  • Agree
  • Like
Reactions: Rpa07 and Midwest
So if after some FRC testing including IR the readings are satisfactory, one could keep the cabling (for my parents remaining lifetime) and renew the accessories. Could you tell me a little more about how this might be done please? Do you have to cut back the cable, splice on new tails and then connect these into the new accessories? Is there a best way of doing it? Afterwards, would one have to do regular FRC testing to check for any deterioration?

From what I've seen and read, once it starts, there's no way of stopping it from coming back, even after cleaning.

However, I do agree with the others, the stress of a rewire could be too much for some elderly people. My departed father-in-law got stressed out, when they got a new washing machine. If you put yourself in their shoes, what would they gain from a rewire?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

marconi

Mentor
Esteemed
Arms
Supporter
~
Joined
Location
London United Kingdom
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
ADVICE PLEASE - SURFACE CONDUIT SYSTEM FOR REWIRE 3 BED SEMI FRC
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
marconi,
Last reply from
marconi,
Replies
43
Views
5,669

Advert