hi ho, i just replaced replaced 8 gu10 50W bulbs in room as were blown. there is 18 on the one circuit plus 3 mini strip lights under benches very likely 18W each, they were all working when i left and when she left room she switched all 3 switches on 1 go and she said the fuse had blown, would you say by her switchen all on one go would of blown the 5A 1361 fuse ?? i personaly think to many but when you add it up its under 5 A

18 x 50W = 900W / 230V = 3.9A
3 x 18W = 54W / 230V = 0.23A so roughly 4A all in, which is under 5A

any input guys before you all go your local niteclub and dance like your up a ladder and fallling
 
u aint just a pretty dude tony are you.... when i was working there today i found half pack of 5A fuses lying on top of cu .
would you say with the fuse keep blowing would destroy the lamps aswell in some way.
 
also, it's common for the fuse to blow when a lamp fails (more so with MCBs). an anti-surge (motor rated) fuse may cure your problem though.
 
well that sounds great telectrix would they fit in to the 1361fuse carrier or am i going to have to change..., i was thinking of changiung the fuse carrier to a 15A one
 
bad idea.15A is a tad to high a rating for 1.5mm T/E . even worse if it's wired in 1.0mm. better would be to split the lighting into 2 5A circuits.
 
isnt 1.5mm rated at 18-20A or something tel. too much work involved in splitting the lighting circuit. ive told them to change to energy efficent lighting (led) just weighing up mu options for monday morning
 
10A fuse in the FCU, would be better. even better would be to replace the GU10 halogens with LEDs. ssimmples
 
But remember a fuse is there to protect the circuit from damage so you still have the problem of an oversuze fuse at the origin of the circuit.......theres nothing to stop someone removing the fcu in future and just relying on the fuse at the board which at 15A is too much for 1mm............
 
1mm can take 16A if i remember right, the circuit is 1.5mm t&e. i aint as expierienced as i think i am so keep them comming sparkys.. where you get a 10A fuse tel, never seen one before or have i, naw i i havent hey
 
good point. glenn. methinks I=P/U is looking for a quick fix. not a good idea. could try a 6A or a 10A MCB though , after a 15A fuse in the board.
 
well i think change the lamps is easies option, what about that fuse that allows inrush currents tel, do they exsist that will fit in 1361 fuse carrier. if i changed to 6A or 10A mcb wouldn't that mean the zs would change and maybe not meet the requirements.
 
i=p/u The steady current drawn by a lamp is when it is at its operating temperature which for incandescent lamps is around 2000 deg C the initial current draw at 25deg C can as as much as 5 -10 times the steady current. So switching all switches together gives a massive surge just like a motor starting current.
Put in the largest fuse permissible for the circuit cable and advise customer to switch the switches one at a time
If you uprate the fuse you need to confirm the Zs still meets the 0.4 disconnection time
 
Last edited by a moderator:
so you with me platty in chancging the 5A fuse carrier to 15A as it is on 1.5mm t&e, its a dr's surgery so they can take instructions and only the sockets are rcd protected
 
was thinking c type breaker too but why 2.5mm for 15A fuse. am i missing something reallly badly here.. do you think would still trip the blow 15A fuse, the type c breaker does sound the pigs ears
 
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK

559.6.1.6 max overcurrent device for normal lighting circuits 16A
 
Last edited by a moderator:
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK

559.6.1.6 max overcurrent device for normal lighting circuits 16A
yep. got it platty (p) 282...thank you. :crazy:
 
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK

559.6.1.6 max overcurrent device for normal lighting circuits 16A

Think a GU10 Lamp holder might not come under that regulation
 
found it, just trying to get to grips with this book as first time looking at it. have you any valuable input to my original post malcom.
 
That is because the new amendment as deleted the reference to the BS 1361 fuse i-p/u and now refer to the BS 88 series

I remember you lost your BRB book if you have the OSG it will be on page 102 table i for 0.4 secs

they are

Zs 5amp 8.4 ohms

Zs 15amps 2.6 ohms

Zs 20amps 1.4 ohms

Zs 30amps 0.81/0.93 depending on you CPC size
 
so am ok in going with the calculation of zs and if is lower than 2.6 ohms i can change to 15A 1361 fuse carrier. or just convince them to change to differnt energy lamps
 
lenny if you out there, have you ever seen of a fuse that acts like a type c mcb its for a 1361 5A circuit thats tripping with the inrush of the halogens??? just asking as i seen you have a fuse shop .
 
well was just about to say that glensarks, when i was looking the other day at sockets when tripped all fuses were bs88 for sockets which were all in one board and then all the lighting is in one board. now all lighting circuits are 5A do i need to change the fuse carrier to 15A and are these easy to get. or could i just get bs88 hbc 5A fuse
 
Dont forget, BS88s are very common in industrial applications and most (not all) but most industrial loads are inductives so my thinking is you will probably be able to get a BS88 thats suitable......
 
aye i want the easiest option as my practical skills on boards are dunce.lol i know having a fair idea is broc.

i can see delay hbc fuses but these are only protected upto 1.5kA,
 
anyone else got any more input as i have to go to this job in morning. just a reminder bs1361 fuse blowing when 18 halogen lamps are turned on. how would you tackle it???

too now i am going to cef in morning to see if i can get 5A hbc fuse and hope delays the start up current needed from blowing fuse and see if that sorts it.
 
Last edited:
just wondering would a 5A bs1361 fuse have different charcteristics to 5A bs1362 fuse???? could this be anything? thanks for your input on this post guys

think they are replacing blowing fuses with the plug type 1362 instead of 1361
 
Last edited:
ok back to this thread. when i was in there this morning looking i seen there is an 6Amcb on the end of the rail. so could i just get the make of that mcb and get a type c in it and remove 1361 fuse carrier and replace with the type c mcb rated at 6A.. does this make sense to you guys. i have no patience is why i get more info each time i go back or isit i have no expierience.
 

Reply to bs 1361 fuse in the Australia area at ElectriciansForums.net

Similar Threads

I
A few months ago I wired a small conservatory, just the standard stuff protected by a 2 way RCD CU. At the time I was asked to quote for a re wire...
Replies
9
Views
1K
DurhamSparky
D
R
Iv been calculation voltage drop. Could some see if what im doing is correct. So from looking in the regs i have found that your aloud 6.9v...
Replies
13
Views
4K
R
My dear nan decided she wanted to upgrade her kitchen before she retires from work. She asked if if could install a few down lights and sink two...
Replies
26
Views
3K
Garythenab
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top