Been racking my brains all day and still can't figure out how a 6mm twin and earth has ended up burnt out as though having more current through than should the scenario

8.5kw/h electric shower
6mm2 t&e in trunking on wall
40a MCB with 30ma RCD Protected

The cable burnt at CU end and MCB has scorch marks

I cannot understand how the 8.5kw/h shower which pulls 36.95a at maximum heat protected by a 40amp breaker has scorch marks and the cable burnt, any ideas appreciated
 
The screw had probably seized and the cable welded itself in due to the heat build up, giving the impression that it was ok.
 
Cheers Jason, hadn't thought of that hopefully it is sorted now nice job for a callout on a sunday "i Smell burning from my fusebox"
 
Been racking my brains all day and still can't figure out how a 6mm twin and earth has ended up burnt out as though having more current through than should the scenario

8.5kw/h electric shower
6mm2 t&e in trunking on wall
40a MCB with 30ma RCD Protected

The cable burnt at CU end and MCB has scorch marks

I cannot understand how the 8.5kw/h shower which pulls 36.95a at maximum heat protected by a 40amp breaker has scorch marks and the cable burnt, any ideas appreciated

Your 6mm^ T+E erection method B is rated a 38 amps ................awfully close to that 37amp threshold, all you need is a semi loose connection, and you will start heating up. Change it to 10mm^ if it's in a trunking
 
10mm is great if only the shower switches were designed for it!!! just had to replace a switch, 10mm cable, only one earth term . in switch, impossible to connect all strands, and this was a MK switch!!
 
ceiling mounted pull switch. even the knock-out in the patress was too small to get outer sheths of 2x 10mm thru
 
For 10mm cable ceiling mounted pull switch I only fit the crabtree 50 amp switch. Perfectly designed for 10mm cable. Also when the cover is removed it removes the neon as well. Nice to see something designed with US in mind.
 

Reply to Burnt 6mm twin & earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello guys n gals, Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run. The...
Replies
14
Views
3K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Correctly closing off a dead twin and earth cable in a loft. My old house used to have radial circuits serving night storage heaters. Those...
Replies
4
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
542

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock