So Zdb is fine for OCPD, what is the issue here?
Discuss C2 or c3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
So Zdb is fine for OCPD, what is the issue here?
So Zdb is fine for OCPD, what is the issue here?
The OP hasnt mention the armourings not being suitable though, just no fly leads from gland to earth terminal. So i imagine this has been checked and complies with the regs.
Unless they're huge cables where the armour is insufficient.
Where's that table?
Conductor CSA | Minimum CSA of SWA to meet 54G | CSA of armour 2 core | CSA of armour 3 core | CSA of armour 4 core |
1.5 | 3.4 | 15 | 16 | 17 |
2.5 | 5.7 | 17 | 19 | 20 |
4 | 9.0 | 21 | 23 | 35 |
6 | 13.6 | 24 | 36 | 40 |
10 | 22.6 | 41 | 44 | 49 |
16 | 36.1 | 46 | 50 | 72 |
25 | 36.1 | 60 | 66 | 76 |
35 | 36.1 | 66 | 74 | 84 |
50 | 56.4 | 74 | 84 | 122 |
70 | 79.0 | 84 | 119 | 138 |
95 | 107.2 | 122 | 138 | 160 |
120 | 135.3 | (131) | 150 | 220 |
150 | 169.2 | (144) | 211 | 240 |
185 | 208.6 | (201) | 230 | 265 |
240 | 270.6 | (225) | (260) | 299 |
300 | 338.3 | (250) | (289) | (333) |
400 | 403.9 | (279) | (319) | 467 |
Conductor CSA | Minimum CSA of SWA to meet 54G | CSA of armour 2 core | CSA of armour 3 core | CSA of armour 4 core |
1.5 | 3.4 | 16 | 17 | 18 |
2.5 | 5.7 | 17 | 19 | 20 |
4 | 9.0 | 19 | 21 | 23 |
6 | 13.6 | 22 | 23 | 36 |
10 | 22.6 | 26 | 39 | 43 |
16 | 36.1 | 41 | 44 | 49 |
25 | 36.1 | 42 | 62 | 70 |
35 | 36.1 | 62 | 70 | 80 |
50 | 56.4 | 68 | 78 | 90 |
70 | 79.0 | 80 | 90 | 131 |
95 | 107.2 | 113 | 128 | 147 |
120 | 135.3 | (125) | 141 | 206 |
150 | 169.2 | (138) | 201 | 230 |
185 | 208.6 | (191) | 220 | 255 |
240 | 270.6 | (215) | (250) | 289 |
300 | 338.3 | (235) | (269) | (319) |
400 | 451.0 | (265) | (304) | 452 |