Discuss Calculating voltage drop on larger SWA cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
R
roukel01
Hi All
A question I've asked many a lecturer and none of them have come up with the same answer.
When looking at the current carrying capacities for SWA cables, from about 35mm onwards you get an r, x, z value. What are these and which one do you use when carrying out voltage drop calculations. is it as straight forward as the smaller sized cables or is it a little more complicated?
R= resistive load
x= inductive reactance
z= impedance
It is when you start to design using cables over 25 /35mm you need to start using all these different co-efficients and of course temperature, grouping etc etc.
To be honest if your just installing a 35mm 40mts for a distribution circuit then you bog standard
m/V/A/m(z) x Ib x L / 1000 would be adequate without those r and x factors needed. It's when you get to 50mm+ the factors are needed for cost saving purposes
Reply to Calculating voltage drop on larger SWA cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Just curious as to when people are calculating volt drop, how close you allow your calculations to get to the 3% and 5% values before you decide...