Hi guys/gals

Directing this question at you that have transitioned already from sparky to pv insatller. I have my first pv install after getting so many queries since the energy price rise and looking to get one under my belt. I want to go in properly and that it is being installed to a high standard. It is a 2.72kw system on roof (garage) system. 8 panels.
Getting a local roofer to do the construction on the roof/set up/ and get cabling safely into attic space. (Do the hook sit on top of tiles or would the tiles need stripping back and cutting around the hooks?
Reading up i belive g98 applies to this install so i can notify dno up to 28 Days after install?
The inverter will go on the block wall next to the consumer unit which has spare rcd ways and into an ac isolator. Also putting a generation kwh inbetween here.
Going to be installing an iboost in the house at the same time on the immersion tank.

Any other tips would be greatfully received :)

BS
 
Make sure you use a DC isolator, be very careful for trapped insulation when terminating, they don't like it at all and the slightest bit will make the iso arc.

As above, always check polarity despite labelling/MC4 arrangement since roofers cannot be relied upon.

Apart from that not much i can think of that you haven't already thunk of, they're relatively simple to install.
 
Check what the inverter needs in the way of RCD protection in the manual, also cabling to it. Some are OK with no RCD (assuming cable run is not in need of additional protection) or even type AC (e.g. ABB inverter, of which I have dealt with before, which was spected to be OK with up to 300mA AC delay) other might demand a type A (all should be now anyway...) or event type B, which will cost a lot.

In fact, if you can avoid the need for 30mA RCD then less risk of it tripping and them not noticing until they see very little cost savings on the electricity bill.

Also it should not be on the load side of an RCD supplying any other circuits if they have dual RCD board, etc.
 
Check what the inverter needs in the way of RCD protection in the manual, also cabling to it. Some are OK with no RCD (assuming cable run is not in need of additional protection) or even type AC (e.g. ABB inverter, of which I have dealt with before, which was spected to be OK with up to 300mA AC delay) other might demand a type A (all should be now anyway...) or event type B, which will cost a lot.

In fact, if you can avoid the need for 30mA RCD then less risk of it tripping and them not noticing until they see very little cost savings on the electricity bill.

Also it should not be on the load side of an RCD supplying any other circuits if they have dual RCD board, etc.
Yes good point regarding rcd, the inverter will be next to the garage consumer unit so i cant see why id need rcd unless MI states it.
Why should it not be on the load side of an rcd in a dual rcd cu?
 
Yes good point regarding rcd, the inverter will be next to the garage consumer unit so i cant see why id need rcd unless MI states it.
Why should it not be on the load side of an rcd in a dual rcd cu?
If the rcd trips the pv system can feed back into the other circuits whereby it won't immediately stop producing when the rcd trips.
 

Reply to Checklist for first solar install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
Is it possible for all or at least most electricians to be trained up in the wiring of solar PV installations, particularly the iBoost or Eddy or...
Replies
3
Views
1K
Hi, I have a 6kw PV with a 6kw Growatt battery and invertor. I have a solar iboost going to the hotwater tank. Recently I had a Ohme Home Pro...
Replies
2
Views
1K
Evening all. I have a question as I can’t get my head around something with solar PV I’m going to be working on a new build in a couple of...
Replies
9
Views
2K
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock