amlu

~
Feb 25, 2011
1,415
402
688
wild east london
Hi :-)
Im finishing rewiring at the moment, place has concrete ground floor, all cables going under the floorboards on first floor or in the loft. There is couple of steel conduits embedded in the building from where consumer unit goes to floor void above. They end up nicely in a metal box where connections can be made (singles in the conduit to twin and earth) Added couple of new circuits and not sure if all will fit in the conduits.
Got 3x 4mm radial, 1x 2.5mm radial and 10mm bonding for water service to squeeze in, to save on space can I run one earth and split it into separate circuits, wonder if thats any good ?
 
It is allowable, It might make testing a problem, but is the conduit not usable as the earth?
 
Conduits may be usable for earth but they are old and rusty, metal enclosure on the other end does not have any terminals, its just a box, plan is to drop another run of 10mm earth single and terminate it with an earth block...
11082015514.jpg
 
Last edited:
Isn't there a limit in the British regs that limits the percentage you can fill a conduit. Current carrying capacities are usually given for cables in conduits assuming a certain airflow and cooling effect, if the conduit is filled tight with wiring you'd usually need to derate accordingly. This is the case with my local SA regs and withsome of the ISO regs.
 
  • Like
Reactions: 1 person
Isn't there a limit in the British regs that limits the percentage you can fill a conduit. Current carrying capacities are usually given for cables in conduits assuming a certain airflow and cooling effect, if the conduit is filled tight with wiring you'd usually need to derate accordingly. This is the case with my local SA regs and withsome of the ISO regs.
Yes there is, but it's rarely complied with.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
wild east london

Thread Information

Title
couple of circuits sharing same earth
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
amlu,
Last reply from
Deleted member 26818,
Replies
5
Views
3,052

Advert