Hey all.

Im new to this forum. Seeing how limited d web is to rectifying any electrical queiries, i thought i might find this useful.

I am a warranted electrical domestic licencee. (Based on IET) and possess a Higher Diploma in Electrical Engineering. I live in Malta (EU) which uses a UK electrical based infrastructure. (TT system).

Just yeaterday as i was looking into a fault at a client, i realised something very strange regarding current draw. I plugged a 0.9KW hairdryer (3.9A @ 230v) into wall socket outlet and clamped live and neutral seperately. L read 4.2A and N read 3.6A. Unless my clampmeter requires calibration what is the reason of this variation???

The worst part is that when i clamped the hot conductor at the consumer unit main DP MCB, it marked that it was drawing 9.2A!!! (Yes, I have deducted the current that was being drawn from the house at that time). That is more than double what it should be marking. I understand that the cables from socket outlet to consumer unit might carry some extra resistance hence draw more current, but surely not to that extent!!!

Can anyone explain this other discrepancy???
 
Re #1: You might want to re-consider what you wrote:

I understand that the cables from socket outlet to consumer unit might carry some extra resistance hence draw more current, but surely not to that extent!!!

What is the accuracy of your ampclamp?

Accuracy-vs-Precision-02.jpg
 
Hey all.

Im new to this forum. Seeing how limited d web is to rectifying any electrical queiries, i thought i might find this useful.

I am a warranted electrical domestic licencee. (Based on IET) and possess a Higher Diploma in Electrical Engineering. I live in Malta (EU) which uses a UK electrical based infrastructure. (TT system).

Just yeaterday as i was looking into a fault at a client, i realised something very strange regarding current draw. I plugged a 0.9KW hairdryer (3.9A @ 230v) into wall socket outlet and clamped live and neutral seperately. L read 4.2A and N read 3.6A. Unless my clampmeter requires calibration what is the reason of this variation???

The worst part is that when i clamped the hot conductor at the consumer unit main DP MCB, it marked that it was drawing 9.2A!!! (Yes, I have deducted the current that was being drawn from the house at that time). That is more than double what it should be marking. I understand that the cables from socket outlet to consumer unit might carry some extra resistance hence draw more current, but surely not to that extent!!!

Can anyone explain this other discrepancy???
Something else plugged in on that circuit? how did you measure the L and N of the Hair drier?
 
The live and neutral current must be equal, so clearly the meter was giving incorrect indications.Either it is faulty, or it cannot handle the current waveform that the hairdryer produces. Some hairdryers half-wave rectify the current to the heating element on low setting, i.e. although the supply is AC the current drawn is pulsating DC. This can cause an AC-only meter to read incorrectly and inconsistently. Even without the overall half-wave rectification, the waveform can be noisy and distorted due to the DC fan motor which also has a rectifier.

You cannot add or subtract currents from the rest of the installation to calculate the expected total reading at the consumer unit, unless they are all in-phase. If there is significant waveform distortion in the hairdryer current, then it will not add algebraically to the current from a true resistive load, for example. Therefore your expected total current may have been in error.
 
Thanks for your replies. However i still find myself confused.

Maybe i need to clarify..

The current reading at the consumer unit which is directly connected to the kwh meter is the actual current draw. The consumer pays depending on the current draw at the kwh meter.

In this case, with the hair dryer turned off, the kwh meter read 2.1A. With the clampmeter left in same place, when i turned the hairdryer on it read 11.3A.(which means that the hairdryer was actually drawing 9.2A!! I.e the consumer will pay on the 9.2A and not on the 3.9A rating of device). When clamped at the socket outlet directly where the hairdryer was connected, it read an average of 3.9A which makes sense according to its rating (900W at 230v.). My question is where is this massive current discrepancy coming from?

(Maybe i need to scrap my clampmeter??)

Thanks again
 
Hi - I don't know what's really going on, but I suspect it's a combination of your meter and how you are using it. For interest you could make up an extension cord and test some loads. Type of load, position of clamp and proximity to other fields may all affect the reading.
 
Please clarify (-even more :) )the it I have highlighted in bold - is it the kWh meter or your ampclamp (or the hairdryer).

In this case, with the hair dryer turned off, the kwh meter read 2.1A. With the clampmeter left in same place, when i turned the hairdryer on it read 11.3A.

and later:

When clamped at the socket outlet directly where the hairdryer was connected, it read an average of 3.9A which makes sense according to its rating (900W at 230v.).
 
Last edited:

Reply to Current draw discrepancy in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
745
I recently had an electrician install a new consumer unit in my cellar. A second electrician, who is subcontracted by my bathroom fitter to carry...
Replies
3
Views
2K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Hello, We have installed equipment at a customer location, (or rather, an external electrical contractor installed it for us). The equipment is...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock