@Leesparkykent its a time delayed one so "should" be ok, you can just see the S on the front of it.... The rcbos are only single pole though so there still isnt perfect discrimination and a fault remaining on the neutral will trip the whole supply... Not a great setup imo...
Agree,could be a problem there
 
My issue with the Lewden boards is the advised torque settings, I have two torque drivers and with either if I torque them to manufacturers settings it has a tendency to damage the rcbo screws.
Do you have the pozi-flat hybrid type driver in your torque set? I do and have never had an issue with the Lewden RCBOs
 
  • Agree
Reactions: cliffed
Think I would have kept the main switch and installed a 63A RCBO, rather than swapping the main switch for an RCD and using a 63A MCB.
 
Yea,the problem is that the 63 amp breaker supplies a Loxone lighting panel,Rcbos in that Panel serves lighting .
So that was the purpose for the 100 ma td Rcd,discrimination for the other rcbos.
 
Trouble is unless they are double pole rcbos then you have provided no discrimination.....
 
I thought it was time delayed ? How will this meet disconnection times ?
Bear with me as I have nothing to do with TT systems and probably lack a lot of knowledge in this area.
Hi - TT disconnection times for a distribution circuit is up to 1 second from Reg 411.3.2.4 :)
 
  • Like
Reactions: Andy78
Hi - TT disconnection times for a distribution circuit is up to 1 second from Reg 411.3.2.4 :)
Cheers for that. Thought I would be missing something. Didn't think the higher times applied to TT.
Every day's a school day.
 
This came with the rcb’os,providing a upfront Rcd is used,it’s ok-ish,I realise discriminating may not be ideal,but what else can you do,on a TT system.

491382E2-7CEE-4D2D-B27D-441EBF1028E6.jpeg
 
This came with the rcb’os,providing a upfront Rcd is used,it’s ok-ish,I realise discriminating may not be ideal,but what else can you do,on a TT system.
Trouble is unless they are double pole rcbos then you have provided no discrimination.....
yea,your talking about the N/E faults that may happen,discrimination will occur when there’s a L/E fault.
Who on earth uses double pole rcbo’s,.
 
Notsure if this uploaded,this came with the rcbo’s

58113504-4C6E-4F47-8493-6B777278655A.jpeg
 
But N/E faults are mighty common? Meaning that one ANYWHERE on that install will cause the upfront to trip loosing the entire installation.

imo that doesnt comply with the regs so either DP rcbos or an alternative design should have been considered.

Also imo on TT with a full rcbo board the 100ma S is not required upfront so youd actually be better off swapping that mcb for an rcbo and the upfronter to a main switch...
 
Last edited by a moderator:
  • Agree
  • Like
Reactions: spark 68 and Rpa07
Ok,but then neutral to earth faults will not be disconnected at all,they will remain,unless DP rcbo’s are used.
The reasoning for the time delay is,discrimination for the lighting panel,which have its own rcbo’s.
 
A neutral fault on that circuit,will trip the individual rcbo’s on the lighting panel,before tripping the time delay Rcd.
 
Something I’ve read:

6B4CEE2B-9840-4750-9C46-DC9CB559A196.jpeg
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
DB installed connected & tested
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
71

Advert

Thread statistics

Created
cliffed,
Last reply from
Rpa07,
Replies
71
Views
8,554

Advert