Before anyone starts slagging me off, or calling me a Muppet that I should know better:shades_smile: I would like to start a discussion regarding Spurs off of a Ring Final Circuit. I have been in this game for a long time now, and always have, and always will spur off of a normal 32a RFC wired in 2.5mm twin with cpc, with the same sized cable, as described in the BGB Appendix 15 page 425.
Looking at the diagram on page 425 it does show that you can use 1.5mm twin with cpc provided you install a fused connection unit prior to the reduction of CSA ie 2.5 down to 1.5 correct?
Now regulation 434.2.1 states, ambiguously that providing the distance is less than 3 meters, you need not fuse down at the point of CSA reduction. I always referred to that particular Regulation with regards to industrial situations for example when you connect to a bus-bar chamber, to provide a feed to a smaller switch-fuse feeding another circuit.
I would like the forum to debate this, as some people are saying that providing the distance is less than 3 meters this ruling can be used in the domestic situation within the RFC situation, ie spur off to a new Socket using 1.5mm cable without fusing down.
As I said not something I would, or have done in the past, sorry for the ramble, but would be grateful for your opinions:clap:
Looking at the diagram on page 425 it does show that you can use 1.5mm twin with cpc provided you install a fused connection unit prior to the reduction of CSA ie 2.5 down to 1.5 correct?
Now regulation 434.2.1 states, ambiguously that providing the distance is less than 3 meters, you need not fuse down at the point of CSA reduction. I always referred to that particular Regulation with regards to industrial situations for example when you connect to a bus-bar chamber, to provide a feed to a smaller switch-fuse feeding another circuit.
I would like the forum to debate this, as some people are saying that providing the distance is less than 3 meters this ruling can be used in the domestic situation within the RFC situation, ie spur off to a new Socket using 1.5mm cable without fusing down.
As I said not something I would, or have done in the past, sorry for the ramble, but would be grateful for your opinions:clap: