You should have seen the confusion in the engineering industry during the change over from Imperial to Cillimetres. Drawings arriving on the shop floor printed on Metric sized paper with Metric dimensions which had been converted directly from the original Imperial dimensions and given to a bloke whose machine and measuring instruments were Imperial. The poor sod (me) had to spend half an hour or so with calculator & pencil changing all the dimensions from Metric back to Imperial before the job could be started. ... Madness!!!

The Grantham grocer's daughter fixed it though when she arrived on the scene with her Final Solution ..... :censored:

I remember it well, although I'd rather forget it.
 
  • Like
Reactions: 2 people
Hi all, you all seem to be having a good laugh. Method of earthing is TNCS in meter cupboard 25m from house, swa 25mm has been run into an isolator with tails out in the meter cupboard, just wondering if an additional earth stake would be required nearer the house. Just want to cover my arse now before the board come out to liven it up.
Thanks for your brains
 
Hi all, you all seem to be having a good laugh. Method of earthing is TNCS in meter cupboard 25m from house, swa 25mm has been run into an isolator with tails out in the meter cupboard, just wondering if an additional earth stake would be required nearer the house. Just want to cover my arse now before the board come out to liven it up.
Thanks for your brains

Good man, you have a sense of humour!

Who ran the SWA and how many cores is it? and why would you want an earth stake? Just asking!
 
Hi all, you all seem to be having a good laugh. Method of earthing is TNCS in meter cupboard 25m from house, swa 25mm has been run into an isolator with tails out in the meter cupboard, just wondering if an additional earth stake would be required nearer the house. Just want to cover my arse now before the board come out to liven it up.
Thanks for your brains
Where is the overload protection for the SWA ???? I asked earlier its a crucial part of the design.
 
Hi all, you all seem to be having a good laugh. Method of earthing is TNCS in meter cupboard 25m from house, swa 25mm has been run into an isolator with tails out in the meter cupboard, just wondering if an additional earth stake would be required nearer the house. Just want to cover my arse now before the board come out to liven it up.
Thanks for your brains

OK....reasonable hat on.
No an additional earth electrode is not required if the entire system is connected to a TNCS earth. There are those who suggest it is a good idea though,as it will reduce the risk of voltages appearing on conductive parts in the (highly unlikely) event of a broken neutral on the supply side.
I have never rodded a TNCS installation myself.
Bear in mind that main bonding in the house will have to meet the requirements for a TNCS system,ie minimum 10mm back to the MET.
 
  • Like
Reactions: 1 person
OK....reasonable hat on.
No an additional earth electrode is not required if the entire system is connected to a TNCS earth. There are those who suggest it is a good idea though,as it will reduce the risk of voltages appearing on conductive parts in the (highly unlikely) event of a broken neutral on the supply side.
I have never rodded a TNCS installation myself.
Bear in mind that main bonding in the house will have to meet the requirements for a TNCS system,ie minimum 10mm back to the MET.



Nice one, thanks for the help. :) the day you stop learning is the day you give up so another thing learned. Thanks :)
 
Overload protection will be in meter cupboard via 100a isolator[/QUOT


a 100A isolator and what OCPD? fuse/MCB or rusty nail?
 
An isolator does not provide any overload protection.

This is what ive been trying to point out from the start several times .... he gives the impression he's using the DNO cutout fuses as upfront protection or he doesn't know the difference between a switchfuse and an isolator.
 
  • Like
Reactions: 2 people
This is what ive been trying to point out from the start several times .... he gives the impression he's using the DNO cutout fuses as upfront protection or he doesn't know the difference between a switchfuse and an isolator.


Oh come on!! .............. He MUST know the difference - he's a spark isn't he?? ......

.............


....... Isn't he?????!!! .. :confused: ... :thinking:
 
This is what ive been trying to point out from the start several times .... he gives the impression he's using the DNO cutout fuses as upfront protection or he doesn't know the difference between a switchfuse and an isolator.

I know you were, but your subtle approach wasn't getting anywhere so I thought I'd try a more direct approach
 
  • Like
Reactions: 1 person
Hi all, you all seem to be having a good laugh. Method of earthing is TNCS in meter cupboard 25m from house, swa 25mm has been run into an isolator with tails out in the meter cupboard, just wondering if an additional earth stake would be required nearer the house. Just want to cover my arse now before the board come out to liven it up.
Thanks for your brains

I do hope that 25mm SWA cable is 3 core, or it won't comply for bonding purposes at the house. That is, the steel wire armouring will not be have a sufficient CSA to comply for bonding purposes, it will only comply as a CPC!!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
do I need an earth stake - metre is 25m from fuesboard
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
59

Advert

Thread statistics

Created
cairns,
Last reply from
Engineer54,
Replies
59
Views
6,532

Advert