Discuss Domestic Bonding test results has o.oo resistance on a 4mm cable do i still upgrade! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Re: Domestic Bonding test results has o.oo resistance on a 4mm cable do i still upgra

has he got it set to IR range?
 
Re: Domestic Bonding test results has o.oo resistance on a 4mm cable do i still upgra

My thoughts also, a low range Ohmmeter would sureky give some other reading that 0.00 Ohms
Pete999

- - - Updated - - -

Surely even
Pete999
 
Re: Domestic Bonding test results has o.oo resistance on a 4mm cable do i still upgra

The main protective bonding sizes are quite clear in the Regs.
However, GN8 goes into detail how a smaller sized MPB can be re-used (not newly fitted) if certain conditions are met.
This has to be recorded in 'Departures from 7671' and 'Comments on existing Installation'.
Being as the minimum size of MPB has been 6mm for a long time (10mm has been typical for what, 18 years?), I wouldn't consider 4mm to be adequate, so would definitely upgrade it.
If it was already 6mm, then I may re-use it in limited circumstances, if, the Guidance Notes are adhered to.
 
Re: Domestic Bonding test results has o.oo resistance on a 4mm cable do i still upgra

hey...bs7671 states 10mm for main bonding, tnc/tncs, stick with the regs to be safe
 
Re: Domestic Bonding test results has o.oo resistance on a 4mm cable do i still upgra

hey...bs7671 states 10mm for main bonding, tnc/tncs, stick with the regs to be safe

Really, what about the bit that has 6mm as the minimum size main bond for supplies other than TNCS?

Don't be a sheep and just follow all the other sheep, read the books and use your brains ability for independant thought!
 
Re: Domestic Bonding test results has o.oo resistance on a 4mm cable do i still upgra

I expect he is using his megger range on his meter not ohms:wink5:
 

Reply to Domestic Bonding test results has o.oo resistance on a 4mm cable do i still upgrade! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hope i find someone who can help me with this one. I have this question on an exam: A continuity test on a protective bonding conductor gives a...
Replies
7
Views
5K
Hello, you all helped me out recently when we had a water leak (mostly in kitchen ceiling), and my landlord's contractor was saying the household...
Replies
7
Views
2K
This is slightly pedantic, so right up my street. I'm filling out an EICR. The sockets are wired in 2.5 (apart from some in the kitchen that have...
Replies
6
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock