Ok, I'm trying to work out whether or not I can put a C50 protected final circuit onto an SNE supply which already has a Ze of .67

Section 411 Table 41.3 (new book) gives me a max value of Zs as .46, so we need to use an RCD...right?? 411.4.9 goes on to say that you can do that for a non time delayed RCD, and use the values for a BS88-3 (.72 which still doesnt get me very far) - so why then does the list in 41.3 include RCBO's to 61009??

Or am I reading the whole thing wrong and need to go back to school?!

R.
 
41.3 refers to the overcurrent characteristics of RCBOs. refer to table 41.1 and 41.5
 
OK, but 41.5 refers to Zs's for TT systems as note 1 refers to 411.5.3 (i) and (ii), both of which refer to TT systems and circuits not exceeding 32A.

Ah! Got it. Reg 411.3.2.3 is the get-out clause for something not covered, so long as it doesn't exceed 5s.

So.... can anyone see an issue with using a 300mA RCD and 50A C type as protection for a 1ph final circuit to a 12kW ground source heat pump fed on 10mm singles in trunking, with a Ze at origin of .67?
 
well, as it's a circuit >32A and cables not buried in walls <50mm, you won't need a 30mA RCD. you would be using the 300mA RCD for fault protection so the max. Zs would be 167 ohms. sounds good.
 
Cheers Tel, I 'knew it should be' but trying to prove it was just defeating me - goes to show, two heads better than one (especially with the morning I'm having!!!).

This is why we went to sparky school and don't do £50 back pocket bungs in the pub. At least we know how to make something catch fire properly!!
 

Reply to Getting confused with a Zs / time - regs in contradiction?? in the Australia area at ElectriciansForums.net

Similar Threads

I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
V
Hey guys, i have started to do some inspecting and testing, i am finding it very interesting although the certification part is a little confusing...
Replies
26
Views
4K
N
Just wanted to say thanks for all your advice and help as I passed my first assessment with an A grade. Quite honestly he didn't stand a chance as...
Replies
24
Views
4K
Please take some time to read through this. It is written by Widdler's father. I found it on a governement website.. It certainly speaks my mind...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock