I have replaced a distribution board. Now in the process of testing circuits and found a 2.5 twin and earth on the cooker circuit.

Now this job will be getting inspected by the NICEIC. Here's the apparent problem:

the 2.5 t+e spur must be joined under the floor board, the client does not want me to rectify it just yet until the circumstance are better, does not want me ripping kitchen laminate flooring up. This is also a job i did for free for friend of a friend so that i have suitable jobs to be inspected.

So I will just write it up on my report and fail. However now I have the issue where I know the cooker circuit has a 2.5mm spur on a 40 amp breaker.

The client has an electrical cooker.

Do I leave 40 amp breaker in with note on test certificate ? What does one do in this situation when client don't want job done even for free. Surely cooker trip on a 20amp breaker.

many thanks in advance.


JS
 
try it full on and clampit. you might be able to fit a 20A MCB.
 
  • Like
Reactions: 4 people
As above. If its pulling over 20A then give it the correct code and then you can explain to the NIC inspector why you have given the code and what the problem is.
 
Do you know what is at the end of 2.5 T&E spur. What is 2.5 cable likely to draw under normal working conditions. ie 1 sgl socket or a fused spur etc. Agree with above with regard down fusing if possible but would read BS7671 Reg 433.2.2 and 434.2
 
You can't code it as your not doing an EICR.
the best thing you can do is remove the fused spur, put cables in connectors, and blank it of, home owner will be safe, and if its a problem they will get you to put it right ASAP, make a note on your cert
 
  • Like
Reactions: 2 people
The problem with fitting a 20A MCB is that if and when the cooker trips it sometime in the future, it will simply get "upgraded" to a 32/40A. I know that's "not his problem", but I'd feel happier doing what chilli says, and blank it off, with the ultimate aim of finding the join and disconnecting it.
 
As you have fitted a new CU you must use the appropriate protective device for the circuit otherwise your work will not comply. As above I think I would disconnect the cooker on those grounds if you feel the load is too great for the circuit..what happens after you leave is the clients business...however I think you'll find if you explain what you are doing and why they will have you back to rectify pretty sharpish..!
 
  • Like
Reactions: 1 person
To reiterate, you should be completing an EIC so codes are not relevent.

You need to decide whether to leave it as is and note on the cert or push the client to agree to fix it.

Welcome to the real world!
 
  • Like
Reactions: 1 person
To reiterate, you should be completing an EIC so codes are not relevent.

You need to decide whether to leave it as is and note on the cert or push the client to agree to fix it.

Welcome to the real world!

Indeed. Get used to NOTHING being textbook (unless you become one of these guys who call themselves electricians and just pull cables in on newbuilds everyday).
 
  • Like
Reactions: 1 person
I did an EICR recently and the cooker hood was fed off the cooker circuit, but there was a FCU in the circuit and I didn't consider this an issue due to the promimity of the FCU to the cooker isolator.
 
I did an EICR recently and the cooker hood was fed off the cooker circuit, but there was a FCU in the circuit and I didn't consider this an issue due to the promimity of the FCU to the cooker isolator.

You mean that it was fused down within 3M of where it joined the larger cable? :)
 
Ahh my mistake for stating you should code it, didn't read the OP properly. Surely before you changed the CU how much testing did you do?
 
You mean that it was fused down within 3M of where it joined the larger cable? :)

I read his post and he does not mention distances or what is on the end of this 2.5
Maybe he is worrying needlessly :sailor:
 
Ahh my mistake for stating you should code it, didn't read the OP properly. Surely before you changed the CU how much testing did you do?

Hard to spot a spur when doing a global test before a CU change. Just one of those "extras" we have to mention to the customer prior to starting the job. :)
At least the op is testing properly, and not just doing the bare minimum as many do after such a change.
 
  • Like
Reactions: 3 people
Ok, there is 6mm to a socket then into the cooker connection unit.

I then do the checks and in the alcove seperating the toilet and the kitchen; is a 2.5 spur in trunking feeding another double socket. This double socket is for freezer and washing machine.

At first glance one would expect that it was spurred from the kitchen ring. This is not the case, it turns out this is also off of cooker circuit. There is no fuse connection unit either. The problem is he was not bothered about even upgrading his board. I asked him so that I had a weighty job for the NICEIC. Now he sees this as a head ake more than a favour; I mean imagine that caring out all this work for free and its not even considered a good thing.

I kind of been thinking though,I am gonna do a Career change. The only love I have left is finding and rectifying the faults.

Thank you for all the replies. I have left the job as it is with a 40 amp breaker, the client is fully aware of the risks. Serious though Applied for few caring jobs. ;)


JS
 
Ok, there is 6mm to a socket then into the cooker connection unit.

I then do the checks and in the alcove seperating the toilet and the kitchen; is a 2.5 spur in trunking feeding another double socket. This double socket is for freezer and washing machine.

At first glance one would expect that it was spurred from the kitchen ring. This is not the case, it turns out this is also off of cooker circuit. There is no fuse connection unit either. The problem is he was not bothered about even upgrading his board. I asked him so that I had a weighty job for the NICEIC. Now he sees this as a head ake more than a favour; I mean imagine that caring out all this work for free and its not even considered a good thing.

I kind of been thinking though,I am gonna do a Career change. The only love I have left is finding and rectifying the faults.

Thank you for all the replies. I have left the job as it is with a 40 amp breaker, the client is fully aware of the risks. Serious though Applied for few caring jobs. ;)


JS


That's like jumping from one thankless task into another.

Respect to you though. ;)
 
  • Like
Reactions: 1 person
Hope nothing goes wrong with it then been left on a 40A breaker, because if you have changed the board, not followed the regs and not notified, if something does go wrong, you better learn not to drop the soap.
 
  • Like
Reactions: 2 people
Don't lose heart mate ! & really lads, scaremongering about prison isnt helping! I think on reflection I would have bunged it on a 32 if its mostly in 6mm , the spurred socket in 2 five is then pretty much same as a spur off a ring, kind of almost complies in a twisted kinda way...
 
  • Like
Reactions: 2 people
How does a radial 2.5 with a maximum current carrying capacity of 27A at best comply with BS7671? You got a reg for that?

sometimes a little fear will help. If he's been a total arse and unreasonable and a generally not nice I would nip back tomorrow telling him I need to put some stickers on the board. Quickly swap to a 20A MCB and wait for the phone call when it trips.
 
As I understand it its only the last socket in 2.5 & all I was saying was it was similar to spurring a single socket outlet from a point on a ring in a single length of 2 five, same effective protection...its there..in 'standard circuits'...
 
40A MCB is not acceptable, end of. You have not "left it as it is", you have "connected it to a new".
So, are you not going through with the assessment now?
 
Been giving this a bit of thought, i take it the kitchen is on the ground floor? Is it not worth going into a carpeted room, and making yourself a hatch to possibly crawl under/ have a good look around?
 
simple solution is to replace the socket outlet for a twin back box, and then put a fused spur on one half of the twin back box, feeding a single socket on the other half, assuming the client can deal with having only as single socket outlet there. If not, fit a snugly chopped out second single socket next to it to replace the lost outlet. I little bit of filler and job done.
 
Been giving this a bit of thought, i take it the kitchen is on the ground floor? Is it not worth going into a carpeted room, and making yourself a hatch to possibly crawl under/ have a good look around?
Whole ground floor is laminated right through to toilet.

To get everyone straight, I am up for what ever It would of took. The client is not wanting me to rip up floor, out of the question. He does not like the idea of putting a 20 amp., called the term " you like creating problems don't you" he said in a joking undertone.

In his eyes his it is working. He has basic knowledge of electrics. It is highly unlikely that the cable will ever be over worked. If it did then there's the rcd. He says :/

i am thinking that maybe I could stick a fuse connection unit where the cable first appears. I can not see there being more than 3 m underneath the floor board. I am certain there will be a JB somewhere.

As for loosing heart, my head is all over the place. I really done some deep thinking today, I prob just keep to inside the circle jobs. Motivation is on a low, prob because last 5 jobs i done for free :/. Turn my website into somewhere to put all these thoughts I constantly getting :/


Thanks for all the comments.
 
Whole ground floor is laminated right through to toilet.

To get everyone straight, I am up for what ever It would of took. The client is not wanting me to rip up floor, out of the question. He does not like the idea of putting a 20 amp., called the term " you like creating problems don't you" he said in a joking undertone.

In his eyes his it is working. He has basic knowledge of electrics. It is highly unlikely that the cable will ever be over worked. If it did then there's the rcd. He says :/

i am thinking that maybe I could stick a fuse connection unit where the cable first appears. I can not see there being more than 3 m underneath the floor board. I am certain there will be a JB somewhere.

As for loosing heart, my head is all over the place. I really done some deep thinking today, I prob just keep to inside the circle jobs. Motivation is on a low, prob because last 5 jobs i done for free :/. Turn my website into somewhere to put all these thoughts I constantly getting :/


Thanks for all the comments.

The problem is Jimmy, you have carried out this work and left it in a possibly dangerous condition. It's not enough to just say "oh well, he doesn't want it doing." It has to be agreed with the client (even if you are doing it for free) that any issues must be sorted before re-energising a circuit. At the very least, you need to put this circuit on a 32A MCB.
 
  • Like
Reactions: 1 person
What if its over 3m from where its jointed to the 6mm?

No not retarded, just putting a case across without getting wound up or abusive for no reason?
 
What if its over 3m from where its jointed to the 6mm?

No not retarded, just putting a case across without getting wound up or abusive for no reason?

MY understanding of this scenario, is a socket outlet spurred from a cooker circuit protected by a 40 amp MCB.

Solution, is change the double socket back box to a twin back box, on one half of which is a FUSED (13A) spur. This then feeds a single socket outlet next to it.

If you can't understand this, go clean toilets. I thought this was a forum for ELECTRICIANS!.
 
What we should really be asking here is the obvious question....Why, oh why didn't you just do a CU change on your own property?
 
  • Like
Reactions: 1 person
Indeed. Get used to NOTHING being textbook (unless you become one of these guys who call themselves electricians and just pull cables in on newbuilds everyday).

;)
As you have fitted a new CU you must use the appropriate protective device for the circuit otherwise your work will not comply. As above I think I would disconnect the cooker on those grounds if you feel the load is too great for the circuit..what happens after you leave is the clients business...however I think you'll find if you explain what you are doing and why they will have you back to rectify pretty sharpish..!
I have, explained.

Thanks for the revelations. Wanted to get this NICEIC quicker, I am a new business. Didn't want to use the " £250" grant I have for handing out leaflets courtesy of Princes trust.

Have two estate agent that like my idea, said they would send my leaflets to all their landlords. Wanted to send the leaflets with a NICEIC badge. Was offering something along the lines of £5 a month all inclusive callout. £40 excess. That was the idea. Also got a £1080 grant of the government and another grant of £540 there abouts. So nah I don't think I am a mug.

What you give you get back. The people I have done work for are all hard workers and good people. So :P .
 
Last edited by a moderator:
;)

I have, explained.

Thanks for the revelations. Wanted to get this NICEIC quicker, I am a new business. Didn't want to use the " £250" grant I have for handing out leaflets courtesy of Princes trust.

Have two estate agent that like my idea, said they would send my leaflets to all their landlords. Wanted to send the leaflets with a NICEIC badge. Was offering something along the lines of £5 a month all inclusive callout. £40 excess. That was the idea. Also got a £1080 grant of the government and another grant of £540 there abouts. So nah I don't think I am a mug.

What you give you get back. The people I have done work for are all hard workers and good people. So :P .

You must have mis-typed this.....£5 a month all in for a call out? Can you please expand and clarify your business plan and background so we can be of more help.
 
You must have mis-typed this.....£5 a month all in for a call out? Can you please expand and clarify your business plan and background so we can be of more help.
£40 excess. The idea would be in the beginning it would be hard. But most of the time the landlord would be £5 a month, like an insurence. The landlord then knows any call out is not going to be no more £40. This is fault scenario.
 
£40 excess. The idea would be in the beginning it would be hard. But most of the time the landlord would be £5 a month, like an insurence. The landlord then knows any call out is not going to be no more £40. This is fault scenario.

Impossible to quote £40 max for fault finding. Sorry, but no wonder you are bankrupt with business plans like this. A bit like 'I WILL MOT your piece of she-ite car for £40, no matter what is wrong with it, I will put it right'.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Clacton

Thread Information

Title
Help with test and inspection.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
69

Advert

Thread statistics

Created
JiMMySnoW,
Last reply from
Geordie Spark,
Replies
69
Views
7,550

Advert