Discuss Is this an error in the "Electrician's Guide to the Building Regulations" in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Reading the "Electricians Guide to the Building Regulations" today (ISBN 978-1-84919-889-9) section 5.7.5 Fixed Equipment, further down the paragraph states:
"Outdoor fixed equipment is not required to be protected by an RCD" That in itself does not ring correct to me I would expect an RCD to be required for all outdoor equipment. It is then followed by "A disconnection time of 0.4s is required for circuits not exceeding 32A". So how is this disconnection time achieved without an RCD?
Is there an error in this wording?
Fixed outdoor equipment in itself may not be required to be protected by RCD, however any associated sockets, wiring methods, or manufacturer's instructions may require this to be present, and it's a good idea too.
Any TN circuit of 32A and under of normal nominal supply voltage is required to disconnect in 0.4 seconds. This is achieved through ADS (automatic disconnection of supply) by keeping the EFLI suitably low to permit this. See table 41.1 and section 411 for further education on the fundamentals.
All sounds fine to me. I think the mention of RCDs is to debunk the myth that just because it's outside, doesn't necessarily mean it needs an RCD. The fact that you thought it might be a mistake in the book justifies its presence.
However, there are plenty of errors in similar publications (the On-Site Guide being of particular note) so it's always worth questioning these things. :)
Your question about how is a disconnection time of 0.4s possible without an RCD is a little more fundamental. I recommend you look over your college notes on earth fault loop impedance and overcurrent protection devices, and/or chapter 41 of the Regs.
It is quite correct.
The requirement is for mobile equipment used outdoors to be provided with RCD protection.
When you consider that our a.c. supply cycles from 0V to +230V, back to 0V then to -230V and back to -0V fifty times a second (50Hz), then you will see that there are two complete cycles in 0.4secs.
This means that peak voltage (and of course amperage) will occur four times (two positive and two negative), which gives a protective device four occasions where peak amplitude can cause the protective device to operate.
With MCBs/RCBOs, usually peak voltage only has to occur the once for the protective device to operate.
Which is why they have an instantaneous operating time of 0.1sec.
A disconnection time oh less than 0.4secs is easily achievable.
Out by a factor of 10 there mind Spin ;) , there are 2 full cycles per 40ms or 0.04 secs (hence the significance of the 40ms ms max rule for 30mA RCDs)
Thanks guys, some interesting reading and the usual banter. The reason I queried this in the first place was I sat an exam last week and one of the questions was:
1) Which of the following statements is correct for a fixed circuit serving a garden:
The apparent correct answer was:
The circuit must be either PELV or protected by an RCD.
I argued with the examiner that all 4 options were incorrect and he said they were not. I so turns out I subsequently was told that the exam centre apologised and that the question was in fact wrong as it is not a requirement that the circuit is either PELV or protected by an RCD.
I recall a question from one of the 2391 exams which asked for the requirements for RCD protection of a circuit in an office.
I did point out to the City and Guilds that there are no requirements for RCD protection for such circuits.
Don't know whether anything was done about it?
You think someone would have to check them thoroughly wouldn't you before sending them out...
There was a time where all the questions for the 2391 were written by one person, which meant that if you purchased that person's books you were virtually guaranteed a pass.
The paper with the question I queried was from after they started using questions from multiple sources.
Reply to Is this an error in the "Electrician's Guide to the Building Regulations" in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
6K
Hi There, Homeowner here with no electrical knowledge, so go easy on me! We've had our garage converted, and coming to the end of the project...
4K