D

DTM20

Hi,<br> <br>I have had an issue with a supply provided by another contractor. We are carrying out an installation on an extension to an existing building/installation. The other contractor has provided the supply to the new area. On there certificate it says limitation on a few key areas. As far as I understand you aren't allowed limitations on an installation certificate, if this is the case is there anywhere this is written down I can refer to. Also there is a limitation on the bonding connection to the main water. Again I assume this means they can't find it, I'm sure the nic would consider this a major non compliance ? Again is there something I can refer to in writing for this. <br>I sympathise with the other contractor as if is an extremely large building and I imagine the bonding is very difficult to find, however I imagine there is no instance where it is permissible to not verify a main bonding connection.<br><br>thanks in advance
 
The electrical installation certificate cannot have limitations on it.
Guidance note 3 under "electrical installation certificate" states that and defects or omissions revealed by the inspection shall be made good and inspected and tested again before the EIC is issued.

For bonding if the connection could not be found then testing for continuity and getting a low reading would be a way of testing to be able to expect that the bonding conductor was connected. (though in a large building this result may be suspect because of the likelihood of parallel paths).

However your installation will also require you to test the bonding so it may become moot if you have done this already.
 
Thanks for the replies gents. I think any responsible contractor would agree the main bonding conductors must be verified. In this case as the supply was provided by others, we wanted their certification to verify the existing installation was satisfactory in terms of bonding, however I suppose this should of been verified at design stage, however this project has been designed by a specialist who I suspect never took the main bonding in to consideration.
 
First off, it doesn't matter a hoot what the NICEIC think, they don't make the rules!!

You say this is a large building that you are adding an extension too, what are we talking about here an office building, multiple dwelling building, factory building?? Does it have it's own distribution TX, Multiple DNO LV supplies (more than one DNO LV service head)??
 
It's a hospital with one dno supply to the building we are adding an extension too. I'm sure it's not acceptable to not verify main bonding or have a limitation on an EIC,in anyone's eyes, not just the NIC's. Just wondering what people's opinions are on here, it's always good to get other sparks opinions on matters like this I find :)
 
The Hospital Engineer (Engineering Manager) will /should be able to officially provide you with this information, as well as any other details of the main electrical distribution system, such a Ze or Zdb values etc...
 
I may be way off but if the main water was running in to the building in plastic pipe then it would be unable to introduce earth potential. In this case it wouldnt need bonding. Despite what niceic say!
 
I have written Lim on EIC's before.

For example, working at a large shopping centre in central London where I wasn't even allowed in the switch room to verify supply details.

I would always try and verify main bonding.

Tin hat on.
 
Well I bought the part p doctor book from niceic book and in ther example of certification I stated .water bonded out of sight under sink, this is in departure is that not what it's for
 
Well I bought the part p doctor book from niceic book and in ther example of certification I stated .water bonded out of sight under sink, this is in departure is that not what it's for
Eh? any chance of that in English mate? Sorry but it doesn't make any sense
 
I may be way off but if the main water was running in to the building in plastic pipe then it would be unable to introduce earth potential. In this case it wouldnt need bonding. Despite what niceic say!

If you are talking about a typical domestic house you may well be correct, but in a multi storey block of flats, or in this case a hospital, the original metallic pipework can very easily become extraneous, from the fabric of the building itself.

Hospitals tend to have a higher requirement with regards to the bonding of metallic services, there are also many more such services that will be found in hospital buildings, medical gases being just one example!!
 
Eh? any chance of that in English mate? Sorry but it doesn't make any sense

Hi trev
Had a few beers lol basically the OP was saying that you cant put any limitations on eic but there is a example in the book i.e author of book could not find bonding clamp but had continuity on pipes. So he just wrote his findings In departure, proving the installation is save but not to 17th regs
 
I may be way off but if the main water was running in to the building in plastic pipe then it would be unable to introduce earth potential. In this case it wouldnt need bonding. Despite what niceic say!

It will though. In a house it will very likely have earth potential through an Immersion or Boiler cpc. Therefore it will become classed as extraneous even if it itself is not.
 
That is not really a deviation as such as the regs says bond external or within 600 before branch pipework blah blah and then goes on to say or where reasonably practicable.....
 

Reply to Limitations on electrical installation certificates in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Is it acceptable to lim on eic for supply characteristics? I had a job in a hospital today and I couldnt gain access to the Switch room and the...
Replies
9
Views
998
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
631
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
280
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
522

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock