on my installation the consumer unit is protected by a BS 88 fuse 100a, i was just looking in the on site guide and it says the rated short circuit capacity is 50 at 415 v.. when doing my PSC i got 1.6 ka and PEFC of 1.4ka does this mean my main fuse is to low to deal with possible prospective fault current?

Thanks as always Chris
 
sure a BS88 fuse has a KA rating of 16.5kA.
 
Yep thats right also
BS1361 type 1 16.5kA
BS1361 type 2 33kA

It all on a really useful chart i got off here a while ago.


We're talking BS 88 here.

In old money a BS 88-2 is 50KA @ 415V, a BS 88-6 is 16.5KA @240V & 80KA @ 415V
 