norwood

Morning guys & Happy Christmas

Id like to start the morning with a little debate over the bonding of metal oil tanks in regards to a PME install and the potential of broken neutrals etc. This one always confuses me because I lot of people have different opinions. I cant test to see if its completely extraneous because I cant shut down the whole school which I would like to do. I have heard of electricians putting a spike in the ground at the tank, is this a normal procedure, could I have your views on this please?

Thanks again for your help
 
If you were to put a "spike" in the ground then you would have caused the oil tank to be definitely extraneous and it would now require bonding back to the MET.
Hmm, well I suppose it saves having to test to see if it is extraneous, but if it wasn't to begin with you have now made the installation more dangerous.

The only way to do this is to test it. If the oil pipe goes underground then it is almost definitely extraneous.

I have just thought that you could put a decent rod in the ground near the supply incomer and test continuity from the tank to the earth rod to see if there it is above or below 22Kohms, this may indicate if it were extraneous, but a lot of work to go to for a measurement.
 
Hi Richard

Its is a pain to be honest, its a little school out in the sticks which we don't normally do a lot of and all the oil boilers/installs I have ever come across have plastic tanks. This is a huge metal one on a concrete slab. The oil line does go underground I just wanted to double check myself. It is a lot of work. It is bonded at the MET as far as I can see but I need to double check.
 
Morning guys & Happy Christmas

Id like to start the morning with a little debate over the bonding of metal oil tanks in regards to a PME install and the potential of broken neutrals etc. This one always confuses me because I lot of people have different opinions. I cant test to see if its completely extraneous because I cant shut down the whole school which I would like to do. I have heard of electricians putting a spike in the ground at the tank, is this a normal procedure, could I have your views on this please?

Thanks again for your help

[h=3]Main Bonding[/h] Main bonding is the electrical interconnection of incoming (metallic) services (e.g. water, gas, and oil pipes) plus any extraneous conductive parts of a building (like the metal framework used in some buildings, or the central heating pipework), to the main electrical earth. This ensures that under fault conditions things like pipework running through a building are not able to take on a dramatically different electrical potential to that of the installation's earth connection. Note this also covers the fault situation where it is the installations electrical earth that is itself introducing the dangerous voltag
 
Thanks Pete. Basically text book stuff which you know already. You just need that second opinion to not doubt yourself because you here other things that electricians make up, specially when reading old reports like I do on a daily basis.

Thanks again
 
Thanks Pete. Basically text book stuff which you know already. You just need that second opinion to not doubt yourself because you here other things that electricians make up, specially when reading old reports like I do on a daily basis.

Thanks again

You are welcome, where in the southwest do you hail from??
 
Sunny Exeter! I have just stumbled upon a half a meter of rubber pipe from where it leaves the tank and connects on to the oil line which go down under somewhere. Its installed in a nice alloy box with a lid. There is a 10mm G/Y at the other end before the tiger loop which they have just taken to the boiler panel, not great.
 
Morning guys & Happy Christmas

Id like to start the morning with a little debate over the bonding of metal oil tanks in regards to a PME install and the potential of broken neutrals etc. This one always confuses me because I lot of people have different opinions. I cant test to see if its completely extraneous because I cant shut down the whole school which I would like to do. I have heard of electricians putting a spike in the ground at the tank, is this a normal procedure, could I have your views on this please?

Thanks again for your help

I can't see why you would want to bond a metal oil tank (assuming that it's located outside). Surely it's any metallic oil pipe that needs bonding (if extraneous) near the point of entry to the building?
 
The idea of having an earth rod at the metal oil tank is to prevent the build up of static with the transfer of liquids. The oil pipe if extraneous needs bonding at the point of entry to the building.
 

Reply to Metal oil tank in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
869
If one of your coworkers suffers a severe electric shock, your first instinct will most likely be to rush to their rescue. But first, pause and...
Replies
2
Views
668
Metal shed In Garden with no extraneous conductive parts House electrics PME supply Garo make a 40a PME fault detection unit for EVs and I was...
Replies
4
Views
2K
Hi, Apologies if this is in the wrong forum. I do have another account on here which I would imagine is not allowed by admins - this account will...
Replies
31
Views
4K
I recently learned the importance of electrical grounding and checked all appliances in my home. Toaster, Microwave oven have 3 prong power cord...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock