Hi guys and girls
I have had a phone call from a friend saying that the socket under the kitchen counter for there washing machine is not working.
I tried a socket tester in it and there is a neutral fault. IRd the circuit and tested all the other sockets. All's fine.
The socket is controlled by an FCU located above the counter the fault is between here and the socket beneath the worktop. The FCU controls the socket and an outside socket. I have tried them individually and there is a fault on BOTH sockets.
I am still in training and there electrician is on holiday any help will be greatly appreciated.
I took it off and checked wiring. It's all wired correctly, load from socket next to it and supply to both sockets. Swapped the fuse to make sure.
As above either neutral as come loose on loadside or fcu is faulty on neutral outfeed
Ok I will swap it for one of the other ones in the kitchen and try again.
Thank you all for your help
By the way while I have you on here can anyone tell me what they think of the 2365 parts one and 2?
as said above. badd connection on N in FCU or duff FCU. as for the last question part 1 comes 1st.
IR for kitchen circuit was above 200Mohms (tested with fuses from fcu removed) so I'm a bit stuck there.
Volt tested as well socket next to fcu was at 243V but at socket in question was at about 12V (forgot to mention that earlier) a socket tester showed a neutral fault (checked it on all sockets in kitchen and front room all working)
I checked the wiring of both sockets in question the FCU and the socket controlling them. All visually and checking the copper is fixed
What do you mean by break down box?
I have checked the continuity between supply socket and load at both sockets in question and there is continuity between all even through the FCU
well...
it dont add up...does it Lee...
check polarity (use a loop tester to do this)...whilst you are at it get a Zpn...see what value you get...
you will/should know if its abnormally high....as you cant be 100% sure that plug in tester is OK....better to have some proper values...
Hi Lee, you say the socket under the worktop and the exterior socket are fed from the load side of the FCU above the worktop, isolate and lock off the circuit supplying these sockets, then disconnect the cable feeding these two sockets from the load terminals of the FCU, all three of them cpc, line and neutral and carry out the tests from there, IR, continuity etc? you should be able to verify where the fault lies. Good luck
Reply to Neutral Fault in the UK Electrical Forum area at ElectriciansForums.net
Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...