As a RCD will limit magnitude to 30mA, is that why supp bonding is omitted when fitted, or am I still hung over
Pict
Pict
 
Yes an RCD will comply to 2 of the situations in Reg 701.415.2 the 3rd will be if you have main protective bonding of the installation as in reg 411.3.1.2
 
So if a sub board serves an area with no extraneous or exposed conductive parts and no incoming services that are conductive, then only the main earth conductor is required??
 
if there is no extraneous conductive parts or metal services what is there to bond?

If there is no exposed conductive parts, in essence you have a class II installation so you may not even need technically an earth conductor, but I have yet to see anywhere apart from very specialized installations, that do not have any exposed conductive parts.

Is this just a general thought thrown out or are you working somewhere like this
 
This is a small guest house, with a sub, fed from a sub, with no RCD protection, installed some 20 years back, SWA incomer from a 32A C type breaker feeding a DB for 1 room, 1 x 32A socket RFC, 1 x 6A lighting with 5 A sockets & 1x 16A Heater circuit, there are 5 boards like this, all rooms have been totally refurbed, all plumbing in in PVC with some copper interconnections, so there is no introduced potential, ZSDB is .19, and all served points in the bath/shower are at .02 to the main earth terminal at DB so the sup bonds are all good,but should the exposed copper pipe be bonded as this enters the bathroom from the service cupboard housing the DB.
Pict
 
Check any copper pipe exposed is in fact an extraneous conductive part simply by using your wander lead attached to MET of the installation and then an IR test on the pipe, it is is over 22KΩ then it's not one and no need to bond.

As there is no RCD protection I would definitely be testing every bit of metal pipe in that room, to make sure it is safe.

Not sure what you mean by served points in the bath/shower are at 0.2, if your saying that there are metal pipes having continuity back to the MET, you will need to bond them as in local supplementary bonding.
 
  • Like
Reactions: 1 person
Sorry what I meant that the light,shaver socket, illuminated mirror, towel rail etc are all at or around .02 cont back to the earth bar,
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

the pict

Mentor
~
Joined
Location
Brodick
Business Name
Devlin Maguire Electrical

Thread Information

Title
No it is not another bonding question,But similar
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
12

Thread Tags

Advert

Thread statistics

Created
the pict,
Last reply from
the pict,
Replies
12
Views
1,380

Advert