Hi, Ive had a NAPIT qualified electrician out to install a new feed to the garage along with a new consumer unit in there. Its a short distance of around 6m and the cable he used was a 16mm NYY cable, it has been directly buried around 300mm depth with yellow warning tape, It goes under a few paving slabs but mostly its a graveled area.

Is this installation totally 100% in accordance with current building regulations/standards?

When he came to quote I asked for armored cable, he even specced SWA in the written quote but on the day I noticed it was this NYY cable. He said its all OK and he has passed the Part P certificate onto my local authority. When I questioned him after the job he said its easier to use and bend and things have changed over the years and this cable is fine to use in the installation. He said there is no price difference too.

What are people's thughts?
 
SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members

James

-
Mentor
Esteemed
Arms
Supporter
Patron
Reaction score
3,999
The NYY cable range includes NYY-J and NYY-O cables. These are widely used European power and control cables designed for fixed wiring installation with a voltage rating of 600/1000V. They can be safely deployed in most applications where mechanical stresses are not anticipated – indoors, outdoors, direct burial underground, in concrete, or submerged in water. When NYY cables are required to comply with the UK wiring regulations BS7671 for burial in the ground, they require installation in a conduit or duct to provide protection against mechanical damage. They are not suitable for installation in concrete which is shaken, vibrated or compressed.

It would look like it may not be suitable for the job.
 

mattg4321

-
Esteemed
Arms
Reaction score
1,334
NYY cable is not suitable for direct burial imo.

However I have seen it done numerous times with no ill effect years later. That said I wouldn’t be too happy if someone used it at my house, especially if I had specified swa.

I’ve just moved house and someone wired a water feature in SY! Some people have some funny ideas.
 

ipf

-
Mentor
Esteemed
Arms
Reaction score
4,947
No, it should be armoured. Hi tuff is OK but shouldn't be laid underground, unless protected.
Armoured cable explains itself......
and the armour should be earthed, protecting the cable and whoever may be involved if any damage occurs.
 

James

-
Mentor
Esteemed
Arms
Supporter
Patron
Reaction score
3,999
NYY cable is not suitable for direct burial imo.

However I have seen it done numerous times with no ill effect years later. That said I wouldn’t be too happy if someone used it at my house, especially if I had specified swa.

I’ve just moved house and someone wired a water feature in SY! Some people have some funny ideas.
not just your opinion,
also mine,
also @ipf
also the manufacturers
also BS7671

Not got many votes to say otherwise either!!
 

ipf

-
Mentor
Esteemed
Arms
Reaction score
4,947
not just your opinion,
also mine,
also @ipf
also the manufacturers
also BS7671

Not got many votes to say otherwise either!!
The bloke must be an idiot or a shyster, coming out with such rubbish.
Disgrace to the trade, I say.

If he won't change it, report it to Napit......and Nipit in the bud!!!!........Hopefully.
 
Reaction score
14
It's even worse if he quoted for SWA in the first place. He really needs to come back and redo this.
I've had an email confirmation now from him that it conforms with current regulations. I really can be arsed with it and whilst Id rather it was SWA he has confirmed it conforms so it seems like it would be a struggle.

I can and will sue him if there is a problem in the future, subject that he doesn't emigrate abroad or something!

As a side question do NAPIT or NICEIC assist you in any way if the original electrician is no longer registered or company dissolved etc/ not trading etc.
 

DPG

-
Esteemed
Arms
Patron
Reaction score
10,002
I've had an email confirmation now from him that it conforms with current regulations. I really can be arsed with it and whilst Id rather it was SWA he has confirmed it conforms so it seems like it would be a struggle.

I can and will sue him if there is a problem in the future, subject that he doesn't emigrate abroad or something!

As a side question do NAPIT or NICEIC assist you in any way if the original electrician is no longer registered or company dissolved etc/ not trading etc.

So he says it conforms. Well, it's up to you whether you believe him, or the opinion of several respected electricians on here.

But bear in mind he quoted for SWA, and you paid for SWA.

And even if it doesn't bother you, there is now a potentially dangerous cable in place.
 
Last edited:

westward10

Admin
Mod
Esteemed
Reaction score
17,948
You need to contact NAPIT now. In complaint situations they suggest you contact the contractor first, you have done this and have proof. NAPIT should now be able to act because that type of cable requires additional mechanical protection if buried according to the UK requirements for electrical installations, BS7671.
 

James

-
Mentor
Esteemed
Arms
Supporter
Patron
Reaction score
3,999
Your concern that it is not up to the correct standards is justified.

so the first question is

Is this installation totally 100% in accordance with current building regulations/standards?

Answer NO, it is not compliant with BS7671 (electrical installations) so therefore it is NOT compliant with building regulations.

When he came to quote I asked for armored cable, he even specced SWA in the written quote but on the day I noticed it was this NYY cable. He said its all OK and he has passed the Part P certificate onto my local authority.

NYY is not armoured, you have been given a product that in this application is inferior to the specification.

They may have passed the certificate onto the local authority for part P compliance but it is not compliant in the first place.

The contractor has made a mistake, feel free to email them a link to this post.
in my opinion, they should just bite the bullet, come back and replace the cable with SWA or if they prefer, install some ducting to run the cable in.

We all get things wrong every now and then. a mistake can be made, it is how we deal with them that sets the good tradesmen (and women) above everybody else.

Best of luck in whatever you decide to do.
 