Concentric cable cannot be used as it only has two cores, line and a PEN. Split concentric cable is permitted however it does not meet the requirements for a cable buried in a wall without RCD protection.
If there is only an isolator at the meter position and no ocpd then it's a problem.
And it's not tails, it should be a distribution circuit.