n180

~
Mar 16, 2012
89
24
83
Been asked to do an eicr on a flat above a shop.

Tails are run in concentric cable from isolator switch by the meter, to the main switch in fuseboard.

Never run into this before so not if this is still deemed acceptable or not? Any advice, reg numbers?

Thanks in advance.

IMG_20190927_103046875.jpg
 
They are not tails it is a cable. Split concentric or concentric.
 
  • Like
Reactions: richy3333
Standard concentric, as you find on the DNO side, is a definite ‘no’ as the neutral is not double insulated.
 
Tails are run in concentric cable from isolator switch by the meter, to the main switch in fuseboard.

Concentric cable cannot be used as it only has two cores, line and a PEN. Split concentric cable is permitted however it does not meet the requirements for a cable buried in a wall without RCD protection.

If there is only an isolator at the meter position and no ocpd then it's a problem.

And it's not tails, it should be a distribution circuit.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Ok to use concentric cable as meter tails??
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
n180,
Last reply from
davesparks,
Replies
3
Views
4,596

Advert