I was changing the consumer unit today and look how the previous person has earthed the main water and gas!
20171113_105334.jpg


I will give them 10 out 10 for ingenuity:confused:

Here's how it looked after i had finished.
20171113_134702.jpg


On a totally different job i was called out to i came across this fitted by a so called electrician.
20171108_135012.jpg

The bottom of the rcd is feeding straight out to the RFC.
How he thought that a 63amp RCD on it's own would comply with regulations is beyond me.I had to removed the enclosure and fit a larger one so that i could fit a 32 amp mcb next to the RCD as it needed.
The guy even charged £330 just to fit that unit!

It saddens me that cowboys like this get away with it and tarnish qualified electricians in the process.:mad:
 
That looks like a really good job. Amazing what some people do. Wonder if they are even electricians or just go under the title.
 
Cable tied to pipework of other services!!!
 
Another couple of uglies :)
Out of interest - did contestant number 2 (how that seems to fit ...) take CPC anywhere ?
 
CPC came out of the bottom of the unit directly into the main earth bar.CPC was a single piece of 1.5mm green/yellow which then connected into the ring cpc's via a 15amp connector seen to the right of the photo.
 
  • Like
Reactions: Wilko
That looks like a really good job. Amazing what some people do. Wonder if they are even electricians or just go under the title.
Done the wonder course Job done
 
  • Agree
Reactions: MJPD29
Nice tidy job mate and a vast improvement, but your NICEIC inspector will have you by the balls for strapping the bonding wires to the services, they are supposed to be independently supported.
Not a criticism btw...just saying cos I got picked up for it once.
 
Never been pulled before for tie wrapping the bonding wires and i've done it for numerous inspections before.What harm can it do.They aren't hot or don't move so i cannot see the problem?
 
What reference method would you call it.
 
Not a criticism at all Bob but with the meter tails going in through the rear and not glanded I'd secure then with clips or small cleats.
 
  • Agree
Reactions: Chivers
Never been pulled before for tie wrapping the bonding wires and i've done it for numerous inspections before.What harm can it do.They aren't hot or don't move so i cannot see the problem?
The NIC did issue guidance on this very thing some time ago, I only have the BRB to hand so the reg number may have changed, but 528.3.3 (proximity to non-electrical services) basically states that where an electrical service is in close proximity to another service it shall be arranged that work on that service does not affect the electrical service. I suspect that is the reg that applies.
 
  • Agree
Reactions: Dave OCD
Not a criticism at all Bob but with the meter tails going in through the rear and not glanded I'd secure then with clips or small cleats.

Cheers mate.The tails are cleated at the back of the board before i fitted it so they aren't going anywhere;)

Is there a definite regulation about not tie wrapping bonding cables to the pipes anywhere?
I can understand not tie wrapping t&e cables but bonding cables?
 
Because in general you wouldn't refer to bonding cables via the reference method so the reply is unhelpful.
 
Other services should not to be used to support our cables

Besides,what would your reaction be if he started strapping his pipes to any cables that happened to be handy instead of using his own clips for support :eek::)
 
I've a question based on OP photo of completed work. The new CU is installed on ply. I recently had my registration visit from my chosen CPS and the guy who came wants the CU I installed to be practically air tight.

I had a garage install with 2 x 2.5mm T&E and 1 x 1.5mm T&E installed down wall in trunking to CU. I channeled the wall out to allow back entry into the CU. The gap between CU and block wall is about 5mm. The inspector told me that it was not good enough and that I should be filling the gap with intumescent foam to prevent air getting into the CU and help fuel a fire.

Now I stood there sort of bemused and wanting to really argue it but thought for a second and asked about IP ratings of CU and if the front of the board should be sealed as the gaps between the MCBs would also be a violation. He was quite adamant about it and was stating that it all changed with amd 3.

Now OP has installed a CU on a flammable material, I wonder what my guy would have to say about that???
 
I've a question based on OP photo of completed work. The new CU is installed on ply. I recently had my registration visit from my chosen CPS and the guy who came wants the CU I installed to be practically air tight.

I had a garage install with 2 x 2.5mm T&E and 1 x 1.5mm T&E installed down wall in trunking to CU. I channeled the wall out to allow back entry into the CU. The gap between CU and block wall is about 5mm. The inspector told me that it was not good enough and that I should be filling the gap with intumescent foam to prevent air getting into the CU and help fuel a fire.

Now I stood there sort of bemused and wanting to really argue it but thought for a second and asked about IP ratings of CU and if the front of the board should be sealed as the gaps between the MCBs would also be a violation. He was quite adamant about it and was stating that it all changed with amd 3.

Now OP has installed a CU on a flammable material, I wonder what my guy would have to say about that???
your cps inspector is a dickwad.
 
I've a question based on OP photo of completed work. The new CU is installed on ply. I recently had my registration visit from my chosen CPS and the guy who came wants the CU I installed to be practically air tight.

I had a garage install with 2 x 2.5mm T&E and 1 x 1.5mm T&E installed down wall in trunking to CU. I channeled the wall out to allow back entry into the CU. The gap between CU and block wall is about 5mm. The inspector told me that it was not good enough and that I should be filling the gap with intumescent foam to prevent air getting into the CU and help fuel a fire.

Now I stood there sort of bemused and wanting to really argue it but thought for a second and asked about IP ratings of CU and if the front of the board should be sealed as the gaps between the MCBs would also be a violation. He was quite adamant about it and was stating that it all changed with amd 3.

Now OP has installed a CU on a flammable material, I wonder what my guy would have to say about that???
The reg only states that the CU should be made of non combustible material, nothing else.
 
In all fairness the inspector probably (but not certainly)exceeded the 5 weeks of some of his applicants.

This whole cps thing just gets worse,time as long since past that it should have been shelved
 
That bonding cable with the crocodile clips in the first picture - it's not some sort of temporary bonding lead put in while a plumber has disconnected some pipes is it?
 
As far as why we now fit metal boards,I was told it was due to the old plastic boards melting and dripping down onto flammable items below the unit and setting them on fire.You DO NOT have to make the board airtight.When AM3 came out I started sealing the back of my boards with fire proof silicone.I was told expressly by my NIC guy that this was not needed.If anyone knows of another reason as to why we have to fit these boards then please let me know:cool:
 
That bonding cable with the crocodile clips in the first picture - it's not some sort of temporary bonding lead put in while a plumber has disconnected some pipes is it?

Would you call 10 years temporary? :eek::eek:
 
At least the mice can get into the back of it for a bit of winter shelter.
 
You all seem to be dissing my tie wrapping the bonding wires but how would you take the wire across and support it? I can still see no practical reason why i cannot do it as i have done.Just because someones NIC bloke says you can't doesn't make it law.If any of the other posts of inspectors is to go by they seem to make it up as they go along.
 
No one is dissing you and I have no interest in what the NICEIC recommend or suggest but the fact is they are not suitably fixed. You could have taken a short section of tube from the right side if the board.
 
But why are they not suitably fixed?What detriment can happen?They look pretty fixed to me.Where is the regulation stating that earth bonding wires have to be fixed separately from the pipe?
 
There are never regulations such as..."An earth bonding conductor must not be secured to a pipe with cable ties". The regulations are never that specific.
I gave you the regulation that I believe applies, in the section 'Proximity to non- electrical services'. It would not be possible for another trade to work on a non electrical service without damage to the means of securing the bonding cable. That contravenes 528.3.3.
(From the BRB...reg number may have changed but it'll still be there).
 
  • Like
Reactions: DPG
You all seem to be dissing my tie wrapping the bonding wires but how would you take the wire across and support it? I can still see no practical reason why i cannot do it as i have done.Just because someones NIC bloke says you can't doesn't make it law.If any of the other posts of inspectors is to go by they seem to make it up as they go along.

The regulations would be one reason, so in doing what you have done you have restricted the maintenance/repair to the installations of other trades.
My other critic is your tails are in free air passing in front of other services, I understand at some point it may be necessary to do this as it taps into the meter/henley joint but would expect to see some form of restraint given the larger distance you have, consider a plumber making alterations to that pipe behind, he's going to be knocking against the tails which unless you correct me otherwise would be acting directly on the the meter/henley terminals.
 
Last edited by a moderator:
  • Like
Reactions: DPG
I've a question based on OP photo of completed work. The new CU is installed on ply. I recently had my registration visit from my chosen CPS and the guy who came wants the CU I installed to be practically air tight.

I had a garage install with 2 x 2.5mm T&E and 1 x 1.5mm T&E installed down wall in trunking to CU. I channeled the wall out to allow back entry into the CU. The gap between CU and block wall is about 5mm. The inspector told me that it was not good enough and that I should be filling the gap with intumescent foam to prevent air getting into the CU and help fuel a fire.

Now I stood there sort of bemused and wanting to really argue it but thought for a second and asked about IP ratings of CU and if the front of the board should be sealed as the gaps between the MCBs would also be a violation. He was quite adamant about it and was stating that it all changed with amd 3.

Now OP has installed a CU on a flammable material, I wonder what my guy would have to say about that???

If you can be arsed, I would be tempted to email your CPS with a general technical question regarding the 'sealing' of A3 CU's with intumescent materials.

When the replies comes back, stating there is no requirement other than maintaining IP ratings, you could then respond with your Assessment experience, and ask them to comment on that.
 
It should be noted no IP ratings are given for the rear of a dist board as it is assumed it will be fitted direct to a flat surface and not raised away from it.
 
If you can be arsed, I would be tempted to email your CPS with a general technical question regarding the 'sealing' of A3 CU's with intumescent materials.

When the replies comes back, stating there is no requirement other than maintaining IP ratings, you could then respond with your Assessment experience, and ask them to comment on that.

:eek: Sneaky
 
It should be noted no IP ratings are given for the rear of a dist board as it is assumed it will be fitted direct to a flat surface and not raised away from it.

Noted. It is amusing how this reg still gives rise to debate. I expect everyone seen Wylex's Wylex launch NMFS Intumescents to further enhance Consumer Unit Fire Safety - https://www.electrium.co.uk/news/wylex-launch-nmfs-intumescents-to-further-enhance-consumer-unit-fire-safety, which they state improves CU safety :rolleyes:
 

I've raised a couple of issues of conflicting advice, given on A3 CU's, by Certsure, The Wire (Certsure) and their Technical. Never really had a conclusive response. Just shows they are human, I suppose, and how ambiguous 421.1.201 is.
 
  • Like
Reactions: DPG
It should be noted no IP ratings are given for the rear of a dist board as it is assumed it will be fitted direct to a flat surface and not raised away from it.
Doesn't the general rule for live parts inside enclosures apply? IPXXB / IP2X (416.2.1)

Basically, if you can't touch live parts with your (British Standard) finger, it's OK.
 
  • Like
  • Agree
Reactions: WillWX and Wilko
Personally I'd have tucked the Tails behind the pipe to the left of the new Board then it could be clipped to the wall and there is also what looks like a ring final floating too. Also I can't see why the bonds on the pipes aren't nearer/next to each other? Where's the MET?

Maybe another photo further back might reveal more.

I'm not a domestic electrician amd my work's not perfect but if i post something criticising previous work I'd make sure mine was spot on.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Blackpool,Lancashire.
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
One way of earthing the pipes.....
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
46

Advert

Thread statistics

Created
Bob Geldoff1234,
Last reply from
Des 56,
Replies
46
Views
4,932

Advert